Hi,

I am planning to install the Tesla home charger and to get max output thinking of using 4/3 MC without conduit. Is it OK to use the cable from the below link?
I am planning to run from unfinished basement to the garage(50 feet), so there will be a place(~10 feet), where it will run between the insulation and Drywall. Do i need a conduit?


Thanks,
rg
 
You can run MC cable exposed and without conduit. But you'd be fine with 6/3 (good for 65A). Or 6/2 even. I had bought the cable for my install from the above vendor. No issues.
Pretty sure (?) 6/3 or 6/2 MC is limited to 55-amps in a home so it cannot be used for a wall connector if you want to get the full 48-amps out of the wall connector as it needs wire rated at 60-amps. And the problem with #4 wire is the maximum size wire for the connection to the wall connector terminals is #6, so you will need address that using a bridge with something like #6 THWN.
 
Pretty sure (?) 6/3 or 6/2 MC is limited to 55-amps in a home so it cannot be used for a wall connector if you want to get the full 48-amps out of the wall connector as it needs wire rated at 60-amps. And the problem with #4 wire is the maximum size wire for the connection to the wall connector terminals is #6, so you will need address that using a bridge with something like #6 THWN.
Incorrect. 6 awg mc cable is good for 65A (technically even 75 A if you’re able to use the 90C ratings)
 
  • Informative
Reactions: Rocky_H
Incorrect. 6 awg mc cable is good for 65A (technically even 75 A if you’re able to use the 90C ratings)
See this link, home wire is usually limited to 60C just like NM-B, isn’t it?


See also

 
Last edited:
See this link, home wire is usually limited to 60C just like NM-B, isn’t it?


See also

No. Only nm-b is limited to 60c. Most others can go to 90, but it’s rare to have 90° rated terminals. 75 is fair game
 
  • Informative
Reactions: Rocky_H
Hi,

I am planning to install the Tesla home charger and to get max output thinking of using 4/3 MC without conduit. Is it OK to use the cable from the below link?
I am planning to run from unfinished basement to the garage(50 feet), so there will be a place(~10 feet), where it will run between the insulation and Drywall. Do i need a conduit?


Thanks,
rg
For a 48A EVSE like the Tesla Wall Connector, all you need is 6/2 MC cable. See Advice for EV Charging in North America
 
Pretty sure (?) 6/3 or 6/2 MC is limited to 55-amps in a home so it cannot be used for a wall connector if you want to get the full 48-amps out of the wall connector as it needs wire rated at 60-amps. And the problem with #4 wire is the maximum size wire for the connection to the wall connector terminals is #6, so you will need address that using a bridge with something like #6 THWN.
Thanks for the reply ….Just curious why we need a Bridge ?
 
Any protocols to follow when using MC cable…especially when pulling the cable into the tesla terminal?
Not really. MC cable is effectively THHN wire preinstalled in flexible conduit. Just make sure you're using the right bushings and that sort of thing. Notably the 1/2" size is the appropriate size even though the diameter of the cable is about 3/4".
 
Thanks for the reply ….Just curious why we need a Bridge ?

Unless this has changed (I went looking for the source but cannot find it, so perhaps this is no longer applicable), the connections in the wall connector are sized for a maximum of #6 wire, so #4 wire will be too large. Thus, you would need to use a bridge in which you connect #4 wire to one side and #6 to the side going to the wall connector. This is moot, of course, as you plan to use #6 wire.
 
Unless this has changed (I went looking for the source but cannot find it, so perhaps this is no longer applicable), the connections in the wall connector are sized for a maximum of #6 wire, so #4 wire will be too large. Thus, you would need to use a bridge in which you connect #4 wire to one side and #6 to the side going to the wall connector. This is moot, of course, as you plan to use #6 wire.
Manual says it can take 4 awg wire
 
1714310918133.png


Page 7 here: https://www.tesla.com/sites/default...ng/Gen3_WallConnector_Installation_Manual.pdf
 
Hi,

I am planning to install the Tesla home charger and to get max output thinking of using 4/3 MC without conduit. Is it OK to use the cable from the below link?
I am planning to run from unfinished basement to the garage(50 feet), so there will be a place(~10 feet), where it will run between the insulation and Drywall. Do i need a conduit?


Thanks,
rg
Use a licensed electrician from your state that will apply for a permit and inspection.
Installing a wall charger that draws 48 amps is a device improperly installed can start a fire, burn down your house, and provide an out for your insurance company not to pay. I'm just sayin
 
Use a licensed electrician from your state that will apply for a permit and inspection.
Installing a wall charger that draws 48 amps is a device improperly installed can start a fire, burn down your house, and provide an out for your insurance company not to pay. I'm just sayin
Sure!!! I am not planning to install myself, Just buying the material and will be using a Licensed electrician.