Unfortunately, the installer, who I like and think is competent, is new to Powerwalls. They've only installed a few and apparently this topic was not covered in their Tesla sponsored training. I think they'll be discussing this with potential clients in the future.
Yes, I carefully thought out the sacrifices to be made operating off the battery at night, with snow on the panels for a few days, etc. I decided I could live with that believing no sacrifices have to be made when the sun is shining. The Tesla website says:
"Powerwall can detect an outage, disconnect from the grid, and automatically restore power to your home in a fraction of a second. You will not even notice that the power went out. Your lights and appliances will continue to run without interruption. If you have solar and Powerwall, then solar energy will continue to power your home and recharge Powerwall. Without Powerwall, solar will shut down during an outage."
No asterisk/footnote about the issue we're discussing. I find the above quote misleading. To me, it means when the sun is shining, no worries, all systems are a go. Tesla says, "Without Powerwall, solar will shut down during an outage." They should also say, "under certain common circumstances, even with PW, solar will shut down during an outage."
I am not sure there is much difference between turning off half of your solar during an outage and having the PowerWall turning off all of your solar half of the time.
I suspect the problem is that because of the mismatch between solar production and Powerwall capacity, the Powerwall shuts the solar down whenever it is generating more than the 5 kW the Powerwall can absorb, even if the state of charge would allow charging. I haven't heard that anyone has gotten curtailing of solar production to work, which means it's on or off only. This means the Powerwall will turn the solar off until the solar production is low enough that it can charge. This might mean there's not enough solar production left to charge back up again.
The micros he has already is on a 20A breaker or two someplace in the system. Unfortunately it would be a manual process to turn it off or the PW could as needed.Heck I’d just wire a switch into the panels and turn it off whenever need be.
You're correct. Because your solar is oversized for 1 PW, it's not going to charge until the solar is below the threshold that 1 PW can accept (minus any house loads). You really should consider taking one of your inverters off of the backup circuit, so that during an outage you can keep the PW topped off.
I think you're using the DC panel rating figure of 320W per panel. The Tesla figure is AC inverter watts. So, the 8.0kW of the two strings should be fine. I'm guessing you have the 600W dual panel micros, so that's 300 AC Watt per panel, so those 25 panels would be 7.5kW. That should work. Just move the breaker for the 13 panel string outside the Tesla Gateway.I have 38 x 320kW panels = 12.16kW system. I'll have to confirm this, but believe they are on three circuits as follows:
13 x 320 = 4.2kW
19 x 320 = 6.1kW
06 x 320 = 1.9kW
Tesla says 1 PW per 7.6kW. If I put the 6.1kW circuit on backup, obviously within limit. If I put 6.1kW + 1.9kW = 8.0kW, that would just be slightly over the 7.6 limit.
Everybody feel free to pipe in. Should I take an inverter or two off the backup? If so, which way should I go? Thanks.
Curious what your house consumption is during the days especially when you have good sun and solar production.
In my limited thinking if the PW charge is 5 kW + house needs at that time would be the point where the solar would be turned on again if it was over generation beforehand. Perhaps that is not the case although solar can both charge batter and supply house at same time.
Question is at what point would the solar be shut down. I suspect when it is over the needs of both, house and battery.
But you can still run the house in a power outage, correct? To me, where the power goes and how the Powerwall manages the solar and the house loads as well as charging are trivial issues. It sounds like perfect is getting in the way of a good solution. I understand the technical issues and it would be better if the GT inverter could curtail but it can only be on or off. Perhaps more updated inverters could modulate or curtail to make this less of an issue. I agree the Tesla installer did not explain it very well, but the PowerWall is doing what it does.In a power outage, my original belief was I could run the house normally as long as the sun is out. Solar would go direct to the electrical draw as it does when hooked to the grid (I understand now it doesn't work that way, but at the time of PW purchase....). The battery would just sit there uninvolved till darkness falls and then jump in to save the day.
My single PW is scheduled for installation on 4/24 and I've found this website to be an amazing source of information - thanks to all who contribute!
I have an existing PV system with 24 microinverter panels and have been concerned about the same issue. But according to this photo, my panels are on two separate two-pole circuits inside the Enphase Collector enclosure. I'm assuming I can turn off one two-pole breaker and shut down half of my panels. Is this correct? Do you have a similar enclosure?
View attachment 517769
I think that is the issue. My understanding is that older microinverters do not curtail or ramp down. They are either on or off. It might be less expensive for the OP to upgrade half his micro inverters than buy another PowerWall.Another solution to this problem is to have your inverters reduce their power during an outage through the microgrid frequency. During an outage your Powerwall will set the local frequency slightly higher which your inverters will notice and "ramp down" production. The Powerwall will dynamically set the frequency - higher than spec when the state of charge is higher or net (production - consumption) is higher, at spec when either are not. This allows your solar production to increase and decrease as the Powerwall charges and discharges with the house load.
I'm exploring designing a battery system to install in my garage that can soak up excess solar production while on backup and then discharge it at night reducing the PW2 discharge.
I'm trying to investigate the issues that are being discussed in this post since the system I want to build might solve the issues here.
Some questions:
What is the per-PW2 charging limit? Is it the 5KW output? If the PW2 has a low charging limit, it creates some problems. Solar Grid Tie inverters are current sources. That means they raises their output voltage until 100% of their capacity is being sunk by the grid. Since the grid is unlimited, a solar inverter can have all its power sunk so everything is ok. It never runs into the situation where the grid is disconnected and it is forced to push its output voltage into dangerous territory well above 240V. But when you add a PW2 into the picture ( or 2-4 of them), things get tricky. If the PW2s cannot sink 100% of the Solar Inverters power, the voltage will rise until the grid tie inverters are in over-voltage and will shut off. But the home usage sinks some of the power but it varies and may not work with all Solar Inverters. For example, Enphase M215 inverters are not split phase. They output 240V so 120V appliances cannot use M215 power directly. But many Solar Inverters do output split phase 120/120 so the home can soak up some power. That complicates the discussion in this thread.
Lets make some simple assumptions to illustrate. Lets say the maximum power a PW2 can soak up for charging is 5KW as in its output specification. Say an application has a real 6KW of Enphase M215 inverters on a single PW2. Lets say the home always draws at least 1KW. In this example, one might expect the PW2 to be able to accept 5KW always and since the home uses at least 1KW, it should be ok right? No because the Enphase inverters cannot power 120V home loads since its not split phase. That means the inverters will keep trying to raise their output voltage to force the grid to sink the power. But there is no grid in backup nor can the home plus PW2 soak it up. If the home plus the PW2 cannot sink 100% of the power produced, the Enphase inverters will shut down.
But if this example uses Solar Inverters that produce split phase, the home plus the PW2 will soak up the power and everything will work correctly. The PW2 will charge to 100% from the solar 6KW minus home 1KW = 5KW until its full and use the 60HZ frequency to shut the Enphase Inverters down. Then when the PW2 is down to 96% or so it will return the 60HZ to exactly 60HZ and the inverters will come back on and the recharge will occur over and over.
Its gets more complicated with the new UL1740 inverters that have the capability to be partially throttled back but I doubt the PW2 can support the variable 60HZ or many people have the new spec inverters. So I believe the behavior of the PW system will vary depending on:
1) What can the PW2 sink while charging - 5KW or more?
2) Do the Grid Inverters on the solar have split phase or 240V only?
I am having 3 PW2s installe:
1) PW2 #1 on one of my SMA Sunny Boy 7000 with about 6KW ( the SMA inverters support split phase)
2) PW2 #2 on another SMA Sunny Boy 7000 with another 6KW ( the SMA inverters support split phase)
3) PW2 #3 on a Enphase M215 system with 18 inverters at about 4KW ( the M215s don't support split phase)
My home always draws more than 1KW which can be powered by SMA split phase support.
Since the 60HZ from the PW2's is common, the PW2's cannot shut down one inverter at a time. If the 5KW per PW2 is a hard limit, I will have a problem if the sum of my 3 inverter outputs exceeds 5KW x 3 minus my home 1KW. So my situation will hit 6 + 6 + 4 = 16KW minus 1 KW for my home equal 15KW. Right on the limit limit if the 5KW charge limit is real. Fortunately my SMA inverters can power my homes 1KW split phase so my M215's shouldn't be a problem.It will be a bummer if on right on the edge and it shuts down at peak power in the summer.
This might explain some of the differences people see. Anybody considered adding say another 5-20KWHr of backup power to supplement the PW2's while in backup for EV charging or other high usage applications?
Thoughts
https://www.tesla.com/sites/default/files/pdfs/powerwall/Powerwall 2_AC_Datasheet_en_northamerica.pdf
- The Powerwall inverter is rated for 5kw continuous but 7kW peak for up to 10s "off grid".
- The Powerwall inverter can handle 100% split phase imbalance.