So I have my 2023 MYLR for a few weeks. Uses only 120v 15amp outlet in the garage for charging. The outlet is a GFCI outlet with downstream connection to another outlet outdoor. Nothing is connected to the outdoor outlet. The ambient temperature in my garage has been pretty stable at around 70deg F. I monitored the surface temperature on outlet vs. The hotest part of the travel connector, which happened to be on the silver/black box around the area where the LED "T-E-S-L-A" indicating lights are. Here is what I found..
Amp setting/outlet temp./travel charger temp.
12A/105deg F/112deg F
10A/98deg F/105deg F
8A/95deg F/100deg F
<8A/pretty much same as 8A
Then I got a 3ft 10ga extension cord and plug into the outlet, then plug the travel charger to the other end of the extension cord, and found the charging temperature dropped quite a bit.
12A/80deg F/88deg F
10A/80deg F/85deg F
<10A/pretty much same as 10A
BTW, the circuit breaker has a steady read of around 85deg F on above cases.
Any one experience the same observation? Tesla adviced not to use extension cord but this finding make me want to use it. Thoughts?
Amp setting/outlet temp./travel charger temp.
12A/105deg F/112deg F
10A/98deg F/105deg F
8A/95deg F/100deg F
<8A/pretty much same as 8A
Then I got a 3ft 10ga extension cord and plug into the outlet, then plug the travel charger to the other end of the extension cord, and found the charging temperature dropped quite a bit.
12A/80deg F/88deg F
10A/80deg F/85deg F
<10A/pretty much same as 10A
BTW, the circuit breaker has a steady read of around 85deg F on above cases.
Any one experience the same observation? Tesla adviced not to use extension cord but this finding make me want to use it. Thoughts?