After waiting on hold for support over an hour and then getting disconnected, not sure if I will ever get through, so trying here.
Need to add a circuit to the load center. Probably 120V 20A. Should the electrician be able to handle this like adding a circuit to any other breaker panel? Any documentation pointers?
Thanks
 
After waiting on hold for support over an hour and then getting disconnected, not sure if I will ever get through, so trying here.
Need to add a circuit to the load center. Probably 120V 20A. Should the electrician be able to handle this like adding a circuit to any other breaker panel? Any documentation pointers?
Thanks

Yes, an electrician should be able to handle that. Just keep in mind the total output capacity of your Powerwall(s) versus the total load.
 
So what I have for breakers are:
Off switch on each solar inverter
Solar feed breakers next to the inverters
Main breaker panel breaker
The powerwall and solar breakers in the load center
All of these should be tripped?
 
So what I have for breakers are:
Off switch on each solar inverter
Solar feed breakers next to the inverters
Main breaker panel breaker
The powerwall and solar breakers in the load center
All of these should be tripped?
* trip main-panel breaker that's feeding the load-center
* trip PW breakers in load center
* trip solar-breakers in load-center
* trip off more if you're not sure.

Check with volt-meter to be sure. Do not short contacts with your volt-meter.