I recently signed a change order for 10.72 kW solar PV system with 2 Powerwalls.
My installer insist that it is ok to have:
16 LG 335 on SE3800H inverter
16 LG 335 on SE3800H inverter
This setup results in DC/AC ratio of 1.41. Each SE3800H is rated to handle up to 1.55 ratio.
Per PVWatts, my annual production is estimated to be 17000 kWh from 10.72 kW system on 1.41 DC/AC ratio.
Reducing the ratio to 1.21 by using SE3800 and SE5000 goes up to 17350 kWh annual production.
My installer says though that changing one of the inverter to SE5000 is not possible since its over the allowed PV/PW total output considering 120% rule.
Is it worth changing the plan/order to chase down 350 kWh clipping per year? Or is it ok since the DC system output is expected to degrade overtime anyway?
Thanks for your insight.