    Exactly! Several folks have attempted to guess but it looks like OP has not returned to clarify things.
     
  2. Dukeybootie

    Dukeybootie Member

    Joined:
    Nov 12, 2015
    Messages:
    179
    Location:
    United States
    Sorry for the confusion -- my understanding of things was limited at the time. I am learning a lot as the responses are coming in, so thanks to all who are participating. The clarification should be whether I need a 400A MSP, now that I have a better idea of the situation.

    Seems like the bottom line is this:
    -there are enough homeowners out there with a large PV system and at least 3 Powerwalls running through a 200A MSP that this is clearly possible
    -depending on individual setups, sometimes a 400A MSP would be required due to existing hardware limitations that could not be bypassed

    Anyway, I did sign a contract a couple days ago with a vendor who said they could use the existing hardware, so no need to upgrade at this time. Will see if this remains the case after a more detailed site visit.
     
    • Like x 2
  3. miimura

    miimura Well-Known Member

    Joined:
    Aug 21, 2013
    Messages:
    5,971
    Location:
    Los Altos, CA
    A generation panel tied to the backup side of the Tesla Gateway can reduce or eliminate the need for a high amperage main panel.
     
  4. Southpasfan

    Southpasfan Member

    Joined:
    Jun 2, 2019
    Messages:
    292
    Location:
    Pasadena
    According to my electrician, who I met with yesterday, a 400 amp main panel is for a major compound with multiple A/C units, a pool, and some other major major amp hog item (elevators in Beverly Hills mansions)

    Three powerwalls can only output 90 amps so that’s no reason. What you ought to do as part of your diligence is to get a meter or borrow one, turn on everything in the house at once, and see what your house pulls. Did this yesterday and we were at 70 amps. By everything it was A/c, dishwasher, clothes washer and clothes dryer, every light, plus open up the refridgerated door so it turns on.
     
  5. Southpasfan

    Southpasfan Member

    Joined:
    Jun 2, 2019
    Messages:
    292
    Location:
    Pasadena
    Also, my 16.32 system, with 35 of the 48 panels in a pure south facing roof in SoCal, only puts out 80 amps through a 125 amp sub panel.

    So 400 amp panel has nothing to do with even the largest Tesla system, it would only apply if there were significant, really significant non backed up loads.
     
  6. sorka

    sorka Well-Known Member

    Joined:
    Feb 28, 2015
    Messages:
    7,588
    Location:
    Merced, CA
    With 200 amps, you're combined loads can well exceed 200 amps. I have 400 amps (800 amps of single pole breakers) coming off my 200 amp MSP. If you have a 100 amp panel, your combined loads can't exceed 100 amps, but with a 200 amp panel NEC Sec 220 has exceptions that allow the combined loads to exceed 200 amps...by a lot.

    Best thing to do is if you have a 200 amp panel is do the 220 load calcs yourself if you're trying to get a handle on what's possible before an electrician shows up.
     
  7. sorka

    sorka Well-Known Member

    Joined:
    Feb 28, 2015
    Messages:
    7,588
    Location:
    Merced, CA
    Is that what I have in their proposal? The powerwall and solar loads are clearly entering some other panel related to the GW2 BEFORE reaching my new 200amp MSP. Otherwise 200 amps wouldn't be enough to handle the existing loads plus the new power generation loads. My 200 amps is just about maxed out on loads when it comes to the 220 calcs.


    Capture.PNG
     
  8. miimura

    miimura Well-Known Member

    Joined:
    Aug 21, 2013
    Messages:
    5,971
    Location:
    Los Altos, CA
    The way the diagram is drawn, it looks like the new Gateway 2 with the internal sub-panel being used as the generation panel. Then, a new 200A panel being used for "relocated loads". No loads at all in the main panel.
     

Share This Page

  • About Us

    Formed in 2006, Tesla Motors Club (TMC) was the first independent online Tesla community. Today it remains the largest and most dynamic community of Tesla enthusiasts. Learn more.
  • Do you value your experience at TMC? Consider becoming a Supporting Member of Tesla Motors Club. As a thank you for your contribution, you'll get nearly no ads in the Community and Groups sections. Additional perks are available depending on the level of contribution. Please visit the Account Upgrades page for more details.