I've been researching electrical line diagrams for a 10kW solar system with 2x Powerwalls and how to incorporate that with 200amp service without derating a main breaker or doing a line-side tap for solar. There's a lot of information and references to bus rating requirements in NEC 705.12(b)(2)(3) which I think I understand, but also claims that using a "generation panel" connected to the Tesla gateway will meet those requirements without requiring any derating, but not explaining why. Generally those posts show one set of the TEG backup lugs connected to a 200amp load panel and the other backup lugs connected to a 200amp generation panel.
For example, this is what my configuration would look like following that:
I understand logically that the Gateway bus can't be overloaded because:
If the load panel pulled more than 200 amps, the load panel OCPD would trip.
If the generation panel was pulling power (e.g., Powerwalls charging from grid) and that combined with the load panel exceeded 200 amps, the service disconnect would trip.
I understand the load and generation panel each meet the NEC requirements individually, but don't understand how the Gateway does. Is it because the 2017 NEC bus rating requirement doesn't explicitly call out feed thru lugs? This is more explicit in the 2020 requirements.
For example, this is what my configuration would look like following that:
Code:
[200amp meter with 200amp service disconnect breaker]
| |
Tesla energy gateway
| | (1st backup lugs) | | (2nd backup lugs)
[200 amp main breaker Load panel] [200 amp main breaker generation panel]
various load circuits 60amp solar, 2x30amp Powerwall
I understand logically that the Gateway bus can't be overloaded because:
If the load panel pulled more than 200 amps, the load panel OCPD would trip.
If the generation panel was pulling power (e.g., Powerwalls charging from grid) and that combined with the load panel exceeded 200 amps, the service disconnect would trip.
I understand the load and generation panel each meet the NEC requirements individually, but don't understand how the Gateway does. Is it because the 2017 NEC bus rating requirement doesn't explicitly call out feed thru lugs? This is more explicit in the 2020 requirements.