The welder doesn’t draw 50 amps.Curious question, for real. You have talked about how the load calculations would be different if it were a welder or an EVSE. I know that the methods are different, but as far as I know, they yield the same number.
It uses 100% value of the non-constant loads + 125% of the constant loads on that branch circuit. It's one outlet with one item, so it's just going to be one of those things on either side of the + sign. The welder you take as a non-constant 50A appliance for 100% of 50A = 50A. A Clipper Creek or somesuch EVSE on that outlet is 125% of 40A = 50A. They are different methods, but I'm not seeing how the 50A or 50A would affect the load calculation differently.
.
.... if whether the new 50A circuit is continuous or not determines whether you need a new panel or not... then you need a new panel. Lets say it was for a welder... and a year later they got an EV. Think they'll do a load calc on their panel before plugging in?
no, but that is irrelevant. You are essentially saying two wrongs make a right.
Also, like I said the quality of the outlet matters.