I recently had my 8.16kW system installed with two Powerwalls. I've been running across threads that talk about minimum string size with different inverters. From what I've found, the minimum string size with the new Tesla inverter is 5 panels. I have a 4 panel cluster running on it's own string, and I'm wondering if this was a design flaw by Tesla. I am pre-PTO and have been monitoring the system - on sunny days it appears to be producing well, however, the last few days we have had a few random cloudy/rainy days here in N. Cal and I'm not sure if the behavior(graph chart)seen in the Tesla app is normal for cloudy days. Yesterday had very sporadic production as you can see in the chart. Layout and screenshots posted below. Any input is greatly appreciated.
4 strings running 4 seperate MPPT inputs with new Tesla Inverter. 2 7 panel strings in front of house and 2 clusters in rear on separate strings:
Normal Day(mostly sunny):
Cloudy Days:
4 strings running 4 seperate MPPT inputs with new Tesla Inverter. 2 7 panel strings in front of house and 2 clusters in rear on separate strings:
Normal Day(mostly sunny):
Cloudy Days: