PG&D Disconnect for what? The PowerWall? I had to have them installed for my SMA inverters.
I was hoping to install two PowerWalls for whole house backup, but I'm just not seeing how they're going to integrate it into my panel. Still, I'd like to be as prepared as possible when Semper comes out for my site assessment on Thursday.
I'd love to hear that I could add a 200A master breaker in the lower left corner but if that were possible then I'm sure the box would've come that way instead of having four 100A breakers in the center of the right half. Perhaps they can take advantage of the fact that the meter lugs are connected to those four main breakers by four wires that could presumably be somehow re-routed out to the gateway (if that's allowed) and back into the main panel to feed the four 100A breakers that make up the 200A panel.
Even if I make it past all of that, then I'm guessing the 100A breakers will likely have to be replaced with something smaller like 70A to accommodate the 120% rule and the fact that I have 15A and 20A solar breakers, plus the two new 30A breakers for the PowerWalls.
View attachment 586079 View attachment 586081 View attachment 586082
Whole home backup will not completely work, but whole home plus the car charger off backup likely work.
Land only a 100A breaker to the GW2, and a 60A remains for the car charger. If you really need car charging while off grid, I recommend a 20A 240V outlet installed separately.
See the top left in bold of the top sticker of your service panel. 100A max branch circuit breaker. 200A cannot be safely taken from this panel bus per its listing.
I recommend you run your load calculations for all the other loads in that panel, except car charger. If they total less than 100A then maybe you just run your whole house on a 100A branch circuit breaker, which leads to the Gateway 2. If you really need charging off grid, you can look at that. Its possible that the car charger set to a lower setting along with all your other loads is less than 100A calculated.
The GW2 also has some functionality in it (Site and Conductor Limits) to prevent that 100A breaker from popping if you temporarily draw more than the 100A breaker can take.
I recommend relocate all the PV, along with the new ESS in the GW2 internal 200A subpanel. Then install a small subpanel to relocate those loads from the MSP to be backed up.
Feeding that MSP bus wont happen easily, and quite difficult to make code complaint. There are non obvious problems to doing this and really you don't have that much load that it makes any sense. I'll guess its about 76A calculated load on your main panel from the alternate method load calculation (220.83.A)