woferry
Member
Seems to me that 60A would (barely) cover the output of 2 PWs (~42A max continuous, ~58A peak), but I suspect charging them might be an issue, since that's up to a 42A additional load in that sub-panel, so unless there's next to no load there right now 60A wouldn't cut it. But bumping up to 100A might be enough for the extra PW load. There is a comms cable that needs to be run from the PWs to the Gateway (which needs to be between all of your backed-up loads and the grid, so unless you're only backing-up your garage it will be much closer to the main panel), I don't know how long that run would be in your setup or what the practical limits are for Tesla. But that's just my thoughts, obviously Tesla needs to be comfortable with it and would have the final say.