For this deployment we are using single circuits to each station. The circuits do share a common large 4 inch conduit/gutter before it branches out to 1 inch conduits for each station. An added bonus of flexible pilot signals is that if a station is too far away, we could just software the limit the station to the calculated capacity, like 68A instead of 80A.
For NEC 310.15(B)(3)(a), wouldn't it seem that 160A would be overkill?
In my opinion, yes, but unfortunately inspectors have to go by the code. The reasoning is the potential heat build-up trapped in the conduit from many circuits carried inside one raceway. It was originally intended to deal with the practice of bringing a bunch of smaller branch circuits through a single huge conduit, but the way it's written makes it apply here too.
(3) Adjustment Factors.
(a) More Than Three Current-Carrying Conductors. Where the number of current-carrying conductors in a raceway or cable exceeds three, or where single conductors or multiconductor cables are installed without maintaining spacing for a continuous length longer than 600 mm (24 in.) and are not installed in raceways, the allowable ampacity of each conductor shall be reduced as shown in Table 310.15(B)(3)(a). Each current-carrying conductor of a paralleled set of conductors shall be counted as a current-carrying conductor.
There are some exceptions: cable trays have a special section dealing with that 392.80), raceways less than 24 in. are exempted as are raceways shorter than 10 ft managing a transition for underground conductors entering/leaving a trench. Armored cables (AC/MC) have special provisions, and XHHW-2 insulated conductors (thicker XLPE insulation) are exempted as well. Not sure if you're using XHHW-2 wire; if not, none of these exceptions seem to apply here.
This is why in many commercial installations you'll see a bunch of parallel conduits running along the wall instead of one giant conduit. You can carry 3 circuits in a smaller conduit (6 current carrying conductors) at 80% of the wire's rating vs. having to reduce everything to 50% for 5-10 circuits.