Im certain that 83hz is a typo, s/b 63hz.
Iq8 inverters can act as both a current power supply and a voltage power supply, but they should never go into voltage mode unless connected to enphase gateway and commanded to do so. But seems like they did and weren’t able to charge powerwall.
But I’m interested in thread, as I’m looking for advice on a better profile that has soft curtail and quicker reconnect time is a plus.
When you reach out Enphase, what do they say is the recommended grid code? I am not sure when quick reconnect became something people were seeking. A much better strategy is to prevent the curtailment from happening so often, rather than hack the grid code.
What are you trying to get? Just a quicker reconnect time? You realize that Tesla sees and records each time the system was re-comissioned. If there is some warranty issue, they may question why the warranty issue, especially seeing the grid code was played with. Its something that otherwise never changes more than once or maybe twice.
If you are curtialing pv production, it would indicate you are off grid, and you have an abundance of PV, such that the batteries cand loads an't take it all.
So assuming you do not have a large EV battery to charge to take some of that power, or an HVAC to run to pre-cool/pre-heat the home to take some of the power, why are you worrying about whether the PV came on 5 minutes sooner since you have an oversupply? If the PV comes on 5 minutes sooner without change to your home demand, that just means it will go back into curtail mode sooner because you still have oversupply of PV.
Also, your other electronic devices don't like to see higher than 63 Hz, and 63 is really their limit. Some devices (insteon) are more sensitive. So in your scenario, your home will be experiencing an out of frequency signal more often, because you want to produce PV sooner and therefore get back to the 63 Hz signal to turn off the PV sooner.
The wild card here is what is your Powerwall system frequency set at? Almost all systems are set to shift to 65 Hz out of the gate and your installer can call tier 2 and have them change the frequency signal if the existing PV equipment will recognize a 62-63 Hz shutoff signal.