Install 50amp breaker in 100 amp subpanel with 60amp breaker in main

This site may earn commission on affiliate links.
I have been charging with 110V outlet for a month now. It's ok for range since I drive 40 miles daily. but it took about 10 hours to charge back to 80% each day. I'm trying to install 14-50 220v outlet myself. My subpanel is 100 amp, but the breaker for it in the main is 60 amp. My question is, can I install the 50 amp breaker in the subpanel? The subpanel currently has a 30amp breaker for AC and a couple of 20 and 15A ones.
Thanks!
I am afraid, you will likely OVERLOAD your house wiring (need at least 200 Amp and thicker wires).
 
I finally decided to get an electrician instead of DIY. He said I can't install 14-50 since the cable going in the subpanel can only handle 80A. He installed 30A. But he put in 10-30 outlet. I forgot that it's obsolete and paid. He did use a metal box and ground it. Will 10-30 outlet work? I saw some people had issues. Is it safe or legal to install 10-30? Should I ask him to replace with 14-30? Thanks!
He may have used a 10-2 Romex to save money on material, the 10-30 is safe for your purpose but it is as stated not to code
 
I finally decided to get an electrician instead of DIY. He said I can't install 14-50 since the cable going in the subpanel can only handle 80A. He installed 30A. But he put in 10-30 outlet. I forgot that it's obsolete and paid. He did use a metal box and ground it. Will 10-30 outlet work? I saw some people had issues. Is it safe or legal to install 10-30? Should I ask him to replace with 14-30? Thanks!
The 10-30 will work fine, but as noted above, it's obsolete and not supposed to be installed on new circuits. In your shoes I'd switch it out for either the 6-30, or, if he ran the extra neutral wire, a 14-30.

One thing that people overlook in these situations is that a 40a circuit can be run to a 14-50 and works just fine with the Gen2 mobile connector at the full 32a charging rate. Sure, a 50a circuit would be preferable, but if it's all that you have capacity for, it's a great option.
 
  • Helpful
Reactions: Rocky_H
I finally decided to get an electrician instead of DIY. He said I can't install 14-50 since the cable going in the subpanel can only handle 80A. He installed 30A. But he put in 10-30 outlet. I forgot that it's obsolete and paid. He did use a metal box and ground it. Will 10-30 outlet work? I saw some people had issues. Is it safe or legal to install 10-30? Should I ask him to replace with 14-30? Thanks!

Probably easier for you just to install the 14-30 outlet yourself, if you were considering DIY before. Its much better and the same price as an adapter.
 
Thanks for the responses. He did run extra neutral. I just asked him to replace it with 14-30. if he can't come by in a week or so (he's an hour away), I'll do it myself. All 4 wires are in the box already.
You might as well get a high quality outlet as well for $36, this outlet has huge V shaped lug terminals with Allen head screws that provide a much improved termination as well as having much heavier contacts for the plug

Bryant 30A 4W Single Receptacle 125/250VAC 14-30R BK 9430FR | Zoro.com

just look at the specs on this beast, 30, 50 and 60 all built with these heavy duty specs, well worth the extra money

https://hubbellcdn.com/literature/Bryant_BSS57.pdf

if you do go this route you also need a different cover plate as the diameter is larger than the cheaper outlets. Hubbell Wiring Device-Kellems Single Receptacle Plate, 2 Gang, Silver SS701 | Zoro.com
 
Last edited:
Probably easier for you just to install the 14-30 outlet yourself, if you were considering DIY before. Its much better and the same price as an adapter.

In the USA, I do not think you can legally install a 40 amp breaker for a 14-50. In Canada, it's legal.

I would install a 30 amp circuit if the main breaker in only 60A. Either a 14-30 if a neutral was installed, or a 6-30 if not.