It doesn't always warn, in my experience.
90 ft of #6 running from a sub-panel with a ???A main and #? wire of ??ft to the main panel is probably enough to cause a pretty substantial voltage drop even with nothing else running let alone normal loads (especially resistive electric aux heat). You're looking at 4-5V drop just in the 90 ft of #6 @ 40A, plus a drop in whatever the run from the subpanel is to the main panel. Plus a drop when adding in the subpanel loads and main panel loads.
My limited information says #6 is good for 50 feet. He's on the edge, at least.
At my garage, I have been charging at 40 amps for two years, and now it only does 30 amps. So I don't think it's the wire, in my case. But 90 feet of #6 is interesting. Off a sub panel. Yeah. Interesting.