Looking for comments on the following.
Summary: PG&E will not allow any changes to the main service panel due to violation of minimum distance from gas service. The existing panel is from 1978 and has no rating labels. Discussion here: PG&E Main Panel Clearance - Help
The solar company was going to install line side taps which was the reason for the main panel change. However, the main service panel feeds a 125A subpanel in the garage which contains all the circuits for the home. The subpanel is fed by 100A feeders from the main panel. The main panel has a 100A circuit breaker.
Why wouldn't a load side tap work in this situation? From what I have briefly read online, NEC 705.12 appears to provide regulations for this scenario. The PV could be fed into the subpanel as long as 125% of the inverter output circuit current plus the rating of the OCPD protecting the busbar is not greater than the ampacity of the busbar. If the current busbar does not have the required ampacity then I could just add a larger one protected by a 100A circuit breaker on the feeder from the main panel.
This seems to fall within the regulations(?)
Summary: PG&E will not allow any changes to the main service panel due to violation of minimum distance from gas service. The existing panel is from 1978 and has no rating labels. Discussion here: PG&E Main Panel Clearance - Help
The solar company was going to install line side taps which was the reason for the main panel change. However, the main service panel feeds a 125A subpanel in the garage which contains all the circuits for the home. The subpanel is fed by 100A feeders from the main panel. The main panel has a 100A circuit breaker.
Why wouldn't a load side tap work in this situation? From what I have briefly read online, NEC 705.12 appears to provide regulations for this scenario. The PV could be fed into the subpanel as long as 125% of the inverter output circuit current plus the rating of the OCPD protecting the busbar is not greater than the ampacity of the busbar. If the current busbar does not have the required ampacity then I could just add a larger one protected by a 100A circuit breaker on the feeder from the main panel.
This seems to fall within the regulations(?)