Great! Thanks for the quick answer
@jjrandorin.
Disclaimer: I am NOT a licensed electrician in any way, shape or form. Those that are DIY'ers and would like to repeat what I'm showing you please do so at your own risk. I won't be held responsible for anybody who injures or kills themselves or others by attempting an installation as shown below.
This honestly is fairly basic. I wanted a manual transfer switch so that if my panels were blown off my roof by a hurricane, I'd have some sort of backup power. If they manage to survive the hurricane, now I have the sun, the powerwalls and the generator to survive on.
This is mostly going to be pictures showing my setup and how I extended the wiring in the gateway to a manual transfer switch and then back over to the backup loads center. The manual transfer switch is designed to backup an entire house or whatever else you may need. The one I used is sold by Home Depot and is called EZ-connect. They're sold in multiple configurations.
The below is my original configuration after installation minus the transfer switch. You can see that the two far left panels are my gateway and backup loads center.
View attachment 708712
Below is a picture of the transfer switch I added myself. I had to redo the wiring from a junction box to the left and installed new liquidtight conduit.
View attachment 708713
Below is a picture of the A/C disconnect going to the gateway. And yes the black plastic cover is removed in the gateway to show the wiring.
View attachment 708714
I used new 3/0 wire to extend the wire from the gateway load lugs to the manual transfer switch. This just show the wire coming from the gateway and passing through the backup loads center on their way to the transfer switch.
View attachment 708715
This shows the wires coming from the gateway through the backup loads center to the manual transfer switch. They enter in to the top of the switch. I then routed the existing wire between my gateway and the backup loads center back over to the backup loads center out of the bottom of the manual transfer switch. Then they are secured in to the top lugs of the backup loads center.
View attachment 708716
The generator plug is wired with #10 wire since I have a 30 amp generator. I wired the neutral and ground directly in the backup loads center. And FYI, all these panels are sub panels so all the grounds and neutrals are separated. The main panel is and should be the only panel that has neutral and ground bonded together. I also bonded any metal conduit fittings to the panel ground.
View attachment 708717
The panel manufacturer. I know the handle looks like it's in the off position but it's actually set to the utility position. It bothers me but that's how the labeling, slot and lever are designed.
View attachment 708718
That's pretty much it in a nutshell. Let me know if you have any questions. Total cost was around $700 or so for the parts and $0 for my time lol.