So, each IQ7+ must be protected by a 20A breaker, with a maximum of 13 units per breakers. But Enphase makes their combiner panel with a built-in Envoy for this purpose, which it sounds like you're planning to use.
That's could depend somewhat on where the Enphase combiner panel is located, what the ambient temperature is in that location, and what length of the circuit is exposed to that ambient temperature. But probably not:
Your minimum breaker size is 42.35 * 125% = 52.9A, which rounds up to 60A. You'll also need conductors with a 75C ampacity of at least 52.9A before temperature correction, and 42.35A after temperature correction.
Since the 75C ampacity of #8 Cu is 50A, you'll need to use #6 Cu or #4 Al (if the Enphase combiner panel has lugs rated for it). That will give you a 90C ampacity of 75A either way, so plenty of headroom for temperature correction, I expect that would be no problem (but still bears confirming with a computation).
Drop 2 microinverters, and now you can use #8 Cu on a 50A breaker, again assuming that 90C ampacity of 55A is sufficient after temperature correction. I.e. that the temperature correction factor is no smaller than 40/55 = 0.727, which means you'd be fine at a bit over 131F. There's something about a rooftop temperature adder, which I've never bothered to read but can be found here (310.15(B)(3)(c):
[Looks like it just requires you to keep the conduit spaced up off the roof at least 7/8" to avoid a big penalty.]
Cheers, Wayne