Anyone with this warning might want to inspect their 14-50 (or other) receptacle.
Lots of threads about bad receptacles, even good ones could be wired poorly with insulation trapped in the connections.
I couldn't agree with this more. Have seen multiple cases where the stranded cable typically used in 14-50 or sometimes even 10-30 plugs becomes loose in the lugs of the receptacle, leading to overheating the plug/wire and melting the receptacle. This type of arc-spark failure doesn't typically overload the breaker and can happen over long periods of time, so the breaker doesn't trip unless it has melted the wire insulation or receptacle plastic to cause a fault. Sometimes the first warning you'll get is just the smell of burning plastic letting the magic smoke out.
Check the tightness of those receptacle lugs periodically, especially if it is in an area that sees temperature extremes.