I just picked up a Coleman Powermate 2500 generator for the price of free.
I cleaned it up and got it running. It powered an electric drill with no problems. But when I went to plug in my Gen 2 Tesla charging adapter with a 5-15 plug, the adapter would just go to 2 red blinks of the T, pause a few seconds, 2 red blinks, and over and over like that.
Is the adapter very sensitive, or does the generator just make "dirty" power? I noticed the generator had a grounding tab on its frame, is it supposed to be connected to a metal rod pushed into the ground or connected to a water pipe or something like that?
I don't have to charge the car from the generator, but I wanted to load test it, as it'll be used for backup power to run the furnace if the power goes out this coming winter.
Here is the manual. The UMC Gen 2 is trying to tell you it can't detect ground. What this really means is that it does not detect 120v voltage potential from the hot to the ground pin. (it is really checking for the ground wire being connected and bonded to the neutral)
https://www.tesla.com/sites/default...bile_connector_owners_manual_32_amp_en_US.pdf
Yes, you must ground the generator. Like a wire from the ground pin/stud on the generator to a good earth ground (cold water pipe). The UMC does not like a 'floating' ground.
This has nothing to do with what the Tesla is testing for. While it is technically a good idea to ground your generator to earth ground, almost nobody does it when using portable generators (it probably also is a code requirement - though I am not sure what code applies - I have heard it is an OSHA requirement to have GFCI in some cases). The Tesla is just testing to make sure there is the expected voltage potential between hot and ground. It is really testing for "bonding" of the neutral and ground.
Check and see if the N and Ground are bonded - they probably are.
Also check the voltage and Hz output of the generator.
They are almost certainly *not* bonded together since he is getting that error. Some generators have these bonded together, others do not. My Honda EU2000i does not. I believe this is because if you use a generator with some kind of transfer panel, you want them separate since the main electrical panel is where they will be bonded. But if you use it stand-alone then you do want them bonded at the generator so that a short from hot to ground will blow the breaker. I think some generators may have a bonding strap you can install to tie them together.
I personally built a plug end that has neutral and ground bonded together. When powering things that want to see the bonding I just tie the two together by plugging in my magic plug (I need to go find a picture of that to post here).
In addition to the grounding and neutral bonding mentioned above, the power waveform will probably not be steady enough for charging a Tesla. They are notoriously picky about the frequency stability. Generally, only inverter generators work. Even then, you need to disable any Eco mode until the car has stabilized the charging current.
Hrm, I don't know how true this is. I have not extensively tried a Tesla on a generator. I have only used mine on a generator once and it was a 30kW natural gas powered generator.
But I will say this: Car chargers are just simple rectifiers that take AC to DC. Rectifiers are all around us and they can be built to tolerate pretty *sugar* power. The little wall wart your router came with is likely rated for between 100v and 240v and can handle 50 or 60hz power. I think the concept of electronics needing good power supplies more applies to things that don't have batteries. Since the rectifiers are just providing power to batteries in the car it is not really the end of the world if the power is not perfect. I think typically the issue is if you don't provide consistent DC power to things like computer chips they freak out, but in charging a car (which also has many microcontrollers running) those chips are buffered by the battery.
I also disagree on the Eco Mode comment as well. Disabling Eco Mode is a solution for dealing with thinks with high surge start currents like electric motors. The generator engine does not have time to react to the huge draw. If you have ever watched a Tesla ramp its current draw on a graph it clearly does it really slowly (it can do this since it is all digitally controlled anyway). I have not tried my Tesla with my EU2000i inverter generator, but I am pretty positive that even in Eco Mode it would have no issues since the generator would just ramp the throttle to compensate.
Now Tesla does say you should not charge off a generator. I don't know why. I used my Tesla as a load bank on a 30kW generator (with all the seat heaters turned on to bleed off energy as I approached a full charge on my battery) and it worked great.
I would love if Tesla would provide more details on why they don't want us using generators. I wonder if there are any technical reasons for it? Or are they more safety/liability related? (or they did not want to bother testing / supporting it?)