Hi - I just purchased a new model Y and now need to install a home charging station.

The challenge is - where to hook into my subpanel?

I have a subpanel (near the garage but not in the garage) that is fed with 8 awg wire and 40 amp breaker at main panel. The main panel is about 80 feet away so I don't want to have to do a "home run" cable. I have available space to add additional breakers on the subpanel.

Can I add a 40 amp breaker on the 40 amp subpanel? I seem to recall that you can do this if you add a direct disconnect in the 40 amp subpanel.

Thanks for your help.
 
Sigh. Glad to hear you're going for a hardwired sub-panel.

However, what you need at this point is something called a "Load Analysis". This is where a cognoscenti (typically, an licensed electrician) takes a look at the main (which, in your case, is 40A for the panel), the other loads (probably a garage outlet and/or a garage door opener), and comes up with a figure that says how many amps you can draw without blowing the main.

I'm not an electrician; but I'd guess that if you have a 40A breaker upstream, putting a 40A circuit downstream may not be such a great idea. But don't listen to me.. or for that matter, other maniacs on the interwebs. Find a licensed electrician, not some, friend-of-a-friend-of-a-friend who'll be over the horizon faster than Jack Splat if something catches afire.

I do have a comment, though: the National Electric Code says that if one has a circuit fused at Yea then, if one has a steady, heavy load, the most that steady, heavy load can draw is 80% of Yea. That's why if one has a 15A circuit for some 120 VAC socket somewhere, the max steady load is 12A, 80% of 15A.

So, in an ideal world, if you wanted to charge your Tesla at its maximum current draw of 48A @ 240 VAC, you'd need a 60A breaker, 60A wire, and a hardwired wall connector from somebody (Tesla or otherwise) that can do 48A steady load. (80% of 60A = 48A.)

Now, that also means that if you actually could do a 40A breaker to a Tesla Wall Connector or some such, the most current that would be allowable would be 32A. (You'd still have to have 40A-rated wire, though.)

If ye electrician says that a 30A breaker is OK, then the Wall Connector would be provisioned for that - and you'd have 24A @ 240 VAC charging.

Now, you've got a Model Y. Last I heard, those run at 280 W-hr/mile. Suppose that you want to put 200 miles on the car. Well, let's look at the charging rates:

  • 240V @ 48A = 11.52 kW. 11.52 kW/(.280 kW-hr/mile) = 41 miles/hour. 200 miles/(41 miles/hour) = 4.86 hours.
  • 240V @ 32A = 7.68 kW. 7.68 kW/(0.28 kW-hr/mile) = 27.4 miles/hour. 200 miles/(27.4 miles/hour) = 7.29 hours.
  • 240V @ 24A = 5.76 kW. 5.76 kW/(0.28 kW-hr/mile) = 20.57 miles/hour. 200 miles/(20.7 miles/hour) = 9.7 hours.
Point is: First, ya gotta sleep sometime. So, all of these times are when you're at home, eating, sleeping, and all that. So, it's all pretty much classified as, "Overnight". Except maybe the last one.

Note that your MY probably has a 333 mile range, when charged to 100%, which you'll likely rarely do: More likely, you'll be at 80%, which maximizes the lifetime of the battery, and that's about 266 miles. I usually charge the cars over here when they get down to a little over 100 miles, and that shortens up the charging time. But it's good to have the numbers in front of one, which is why I did those, above.

A couple more comments about cost. Note that with a 40A breaker the most you'll be doing is 32A. As it happens, the Tesla Mobile Connector (TMC), available over at Tesla, can be rigged with the right kind of plug and all to run on a 40A circuit; so, in theory, one could run down to Home Depot or something, get an appropriate socket, pay something nominal for that, pay $250 or so for the TMC, and be running for cheaps.

I'm here to warn you against that. First, the Home Depot specials are not industrial gauge, and the forum here has a number of pictures of consumer-grade connectors that have gone all melty and fire hazardy. An industrial grade socket costs around $150 or so.

Worse, if you're putting one of those sockets in your garage, modern electrical code calls for a GFCI breaker. Those are upwards of $200. So, between buying the TMC, a GFCI breaker, and an industrial grade socket, never mind all the labor and such, you'll be over $500.

On the other hand, A Tesla Wall Connector can be found at Tesla for $450 and other companys' products for similar. They all come with a GFCI built in, so all one needs is the wire (which both solutions use) and a straight breaker, which is cheaper by far than the GFCI type.

Depending upon the State you live in, there's sometimes incentives to have a Wall Connector that reports back to some Mothership or other to let them know how much energy you're using to power your car; in which case, a discount may come your way. At least in NJ, if one is doing that, then the Mothership, whoever they are, posts a list of Acceptable Wall Connectors that can do that thing. So, that may drive the decision of Which Wall Connector to get.

Finally, and I want to emphasize this: Everything in the NEC and local codes is about Taking Care of The Heat. Run current through a wire; all wires have resistance; power in a wire (just like in an electric stove burner) goes as current*current*resistance. Unlike an electric stove burner where one wants the element to glow dull red at times, the NEC is all about keeping the temperatures of the wires, sockets, breaker elements, and such like far, far away from anything that might cause such an element to get warm enough to degrade the insulation around that element. We're talking fire, life, and death here. So, don't take any wooden nickels and stick to licensed electricians, unless >you've< got that expertise. If you do, my apologies.

Have fun!
 
  • Like
Reactions: jboy210 and brkaus
If the sub panel is fed by a 40 amp line then a 40 amp circuit for the EVSE is likely too much because it doesn’t leave any room for other electrical loads.

Depending what else runs off the sub panel you might be able to do a 30 amp (24 amp charging) or 20 amp (16 amp charging) circuit for the EVSE.

Best bet is to consult an electrician of course. You also won’t be able to up the breaker size to the sub panel without running a new line. 8awg is only good for up to 40amp.
 
  • Helpful
Reactions: Rocky_H
Look into load management. There is an accessory device for the Universal Wall Connector that measures the upstream current and can modulate the Wall Connector to remain within the upstream limits. If you have loads on the sub-panel that are only used intermittently, you might be able to put a 40A breaker in the sub-panel and have the load management keep your total draw within the 40A upstream circuit.
 
Look into load management. There is an accessory device for the Universal Wall Connector that measures the upstream current and can modulate the Wall Connector to remain within the upstream limits. If you have loads on the sub-panel that are only used intermittently, you might be able to put a 40A breaker in the sub-panel and have the load management keep your total draw within the 40A upstream circuit.

Here is the Tesla information related to Dynamic Power Management

OP, note that benefit would depend on how much you drive. For some a redgular outlet is enough (especially with a garage to protect the car from the elements). For many a 240V 20A circuit is enough.
I charge my Kona EV using a 30A circuit for 24A charging and that's more than enough, so a 20A circuit would also be a enough, but I'd need to plug in a bit more often.