@sgreenstonenj Please read this too, since I realise that your original question was still ambiguous. The ratings of your wiring and circuit breaker are not what amperage you can pull over the wires if you want to comply with the electrical code, IIRC.
Does your Mini also do 240V charging? What is there from its L2 charger to your main 240V connection?
For 7.7kW, you need 32A. If you want to really pull 32A you'd better have 40 Amps wiring and a 40 Amps breaker on the shared 240V connection...if you have a 32A circuit breaker it's usually not recommended to pull more than 24 Amps over the connection.
If you have a 240V 40 Amp *breaker* IIRC electrical code means that you can't put anything except the SR+ Tesla on that circuit. Even if you put a LR on there if you use the correct adapters or HWC settings you won't be charging any faster, it's already maxed out at 7.7kW.
So I'll need to clarify, since you didn't mention whether in your original post you meant the amperage you wanted to pull over the wires or the capacity of the circuit breaker.
For an SR+ you want to pull 32A from the wall at 240V, which means a NEMA 6-50 or NEMA 14-50 plug and a 40 or 50 amp circuit breaker, IIRC (and you'll need to buy an extra adapter if you want to use the UMC that comes with the Tesla).
If you have a 32A circuit breaker then you probably have a NEMA 16-30 plug, and the SR+ will be limited to 24 Amps (giving you 5.7kW for charging).
If you currently have a NEMA 6-20R plug for the Mini and you want to use that for the Tesla, the adapter will limit amperage to 16A, so you'll be charging at only 3.8kW (i.e. at the speed of a L2 charger for the Mini, but with a much larger battery.)
If you have a 40 Amp breaker, then on that one 240V circuit behind the breaker you cannot safely charge both a Mini with a L2 charger and a Tesla SR+ at max amperage (3.5kW + 7.7kW =11.2kW). You'd have to either move the Mini to a household socket, have two circuits, one 60A breaker circuit, or limit the amperage on one or both cars.