Going back to the OP, if your final load calc comes out to 200A or less, and you are OK with limiting your total inverter capacity to 200A (via the GW CT-based feature), then I believe you can do what you propose without any new panels.
Namely, you can set up a 200A feeder with the following connections in order starting at the service disconnect:
200A service disconnect
Gateway
200A Spur to load panel 1, which needs a 200A main breaker
200A Spur to load panel 2, which needs a 200A main breaker
CTs for monitoring inverter current, limiting it to 200A
200A Spur to generation panel 1
Generation panel 2
That is, you could set up a really big junction box with (5) circuits coming into it: grid/GW, load 1, load 2, generation 1, and generation 2. The neutral and ground conductors just all get connected with 5 port Polaris-type connectors. For each hot you could use a 3 port Polaris and a 4 port Polaris, along with an internal jumper (short wire segment that doesn't leave the box). The 4 port connector gets grid, load 1, load 2, and jumper. The CTs go on the jumper. And the 3 port connector gets jumper, generation 1, and generation 2.
[Actually if the CTs are physically large enough to put (2) 2/0 Cu wires through, you could use 5 port Polaris connectors on the two hots as well, and just put each CT on both generation 1 and generation 2 conductors of a given leg. But if only (1) 2/0 Cu wire fits through the CT, you'd need to use a jumper like I described.]
Pretty sure that complies with the feeder tap rule in 705.12(B)(1). And the stupid thing about 705.12(B)(3) is that if you replace the Polaris connectors with busbars, and the connections with 200A breakers, it doesn't comply. Even though electrically it's equivalent.
Cheers, Wayne
Namely, you can set up a 200A feeder with the following connections in order starting at the service disconnect:
200A service disconnect
Gateway
200A Spur to load panel 1, which needs a 200A main breaker
200A Spur to load panel 2, which needs a 200A main breaker
CTs for monitoring inverter current, limiting it to 200A
200A Spur to generation panel 1
Generation panel 2
That is, you could set up a really big junction box with (5) circuits coming into it: grid/GW, load 1, load 2, generation 1, and generation 2. The neutral and ground conductors just all get connected with 5 port Polaris-type connectors. For each hot you could use a 3 port Polaris and a 4 port Polaris, along with an internal jumper (short wire segment that doesn't leave the box). The 4 port connector gets grid, load 1, load 2, and jumper. The CTs go on the jumper. And the 3 port connector gets jumper, generation 1, and generation 2.
[Actually if the CTs are physically large enough to put (2) 2/0 Cu wires through, you could use 5 port Polaris connectors on the two hots as well, and just put each CT on both generation 1 and generation 2 conductors of a given leg. But if only (1) 2/0 Cu wire fits through the CT, you'd need to use a jumper like I described.]
Pretty sure that complies with the feeder tap rule in 705.12(B)(1). And the stupid thing about 705.12(B)(3) is that if you replace the Polaris connectors with busbars, and the connections with 200A breakers, it doesn't comply. Even though electrically it's equivalent.
Cheers, Wayne