FWIW, both of my AC units are powered through the powerwalls (2) and it's been working like a champ so they can definitely do it.
You can install our site as a web app on your iOS device by utilizing the Add to Home Screen feature in Safari. Please see this thread for more details on this.
Note: This feature may not be available in some browsers.
So I was doing more tinkering today and I think this might be a case of a bad power wall.
Today I noticed that I wouldn't discharge more than 5kW at any given time. I went out to look at the powerwalls and only one was pulsing (Powerwall enabled and charging or discharging - from the manual).
So as a test I disabled the one powerwall that was pulsing and I left the other online.
The only concern is that the malfunctioning powerwall is the second in the comms wire daisy chain, so hopefully the first powerwall doesn't need to be on for things to work on the second.
I just set this up and changed to self consumption with 100% backup, we'll see how long it takes for the config update to roll out to the gateway.
If any one has any other tips on how to isolate if a powerwall is working or not I'm all ears!
FWIW, both of my AC units are powered through the powerwalls (2) and it's been working like a champ so they can definitely do it.
I'm fascinated by the AC compressor mods that heat the pool with the waste heat. In certain climates that tech must be very efficient.
Do you have anymore info on this? This would be great for my pool here in California
I would request they charge the design to include the AC, especially with 4 Powerwalls.My 4xPowerwalls are just being installed this week and I just found out that my AC units are actually not hooked up to the PowerWall. It is kinda of a bumper as I was planning to use the AC during peak rate hours from the stored charge.
My 4xPowerwalls are just being installed this week and I just found out that my AC units are actually not hooked up to the PowerWall. It is kinda of a bumper as I was planning to use the AC during peak rate hours from the stored charge.
Even if your AC units are on the other side of the gateway you can still run them from the Powerwalls when the grid is up. But if the grid goes down and you are running the house in backup mode they wouldn't be able to run. (At least that is my understanding.)
The Powerwall runs in one of two modes:
Island mode (the grid is out). Only loads on the Powerwall side of the Backup Gateway can get power. The CTs are not involved in how the Powerwall works in this mode, its inverter just provides a stable reference voltage and provides or accepts power as required to balance the microgrid, instantaneously.
Grid-tie mode. Absent CT info, the Powerwall would never discharge in this mode. With self-powered mode or advanced time control, and CTs monitoring household consumption, the Powerwall can choose to discharge to offset the measured consumption. But this doesn't necessarily happen in instantaneous balance, and it doesn't have to, as the grid is providing the stable voltage reference and will make up or absorb any discrepancy.
So the upshot is that when the grid is up, if the CTs are configured to measure the HVAC usage, or any other load on the grid side of the Backup Gateway, the Powerwall will recognize the consumption and can discharge to offset it if its algorithm decides to do so.
Cheers, Wayne
Sounds like the two Powerwalls alone don't have enough surge power capacity (14 kW) to start your AC, but that once you add in 7.6 kW of solar power, you get enough available power to start the AC.
Cheers, Wayne
It should be on the AC nameplate as LRA (locked rotor amps). Very hard to measure without a scope and shunt as it lasts only a few cycles.
Most of the big name US systems need a lot of amps to start up, but still run at full speed. These multisplit systems, like the Fujistsu in the pic in the thread can start off as low as 5A and then gradually scale up to full speed as needed, and are much more efficient too.
If you want to drive AC from PW's and are doing a new build or replacing AC, take a look at the Mitsubishi, Daikan or Fujitsu gear. A better fit for PW's.
thx
mike
I do have the name plate rating, but I also have a soft starter attached to the condenser.