No, it doesn't have PEN fault protection. That's a UK requirement for fixed installations. The biggest risk is if the socket you are plugging into (or other sockets in a ring) is not connected securely or has other faults, leading to high temperatures and potential fire. If you want to use a granny charger regularly then it's best to have a separate circuit for the socket. With a UMC, I'd be tempted to have a (switched) commando socket installed and buy the commando plug for the UMC. UK 13A sockets can't really be relied upon to run 10A for hours on end. A good installation will cope but needs keeping an eye on. A bad one can be dangerous.Hi
Does the Tesla UMC have open PEN protectionn or other safety features? Asking becasue I want to use it routinely until I get a proper charge point innstalled (probably in the next house at this rate).
Cheers
JonB
Yes, you are correct re: electrician installations of Commando sockets. He is coming round this afternoon. Too bad I told him what the socket was for!
Of course, I could just tack on a Commando myself (to my garage ring's consumer unit which is some 50m from the consumer unit in the house) and linit it to 16A... but I'd always be worried. I do wonder if in-garage EV charging is treated as if it were outside from the regulation POV.
True, inside is inside. But Edition 18 of the regs effectively says that all EV charge points must be fitted with PEN fault protection (either in the charge point or separately) or with a ground rod / mat. There's no distinction between whether the charge point is inside or outside.I'm pretty sure inside a garage is regarded as inside.
I was told the same thingI'm pretty sure inside a garage is regarded as inside.
That is exactly why. If I remember correctly, there are 10s of cases of PME failure each year in the UK.I'm unclear why Edition 18 is so concerned, unless of course the authors believe that PME systems are not to be trusted.
Thanks for explaining!That is exactly why. If I remember correctly, there are 10s of cases of PME failure each year in the UK.
On a 3 phase distribution system using PME the neutral / earth can (and does) go to a high impedance and the houses on the three phases will all keep working, with the return being made through the other phases through the other houses. EVs are about the only large metallic objects connected to earth standing outside in the rain. If the PME goes high impedance (not necessarily totally open circuit) then the car body can go well over 70V - and to full mains voltage if the PME is totally cut.
Of course, when this happens any earthed metal chassis inside the house (such as boilers or AGA cookers) will go to the same voltage and people can get a shock. But its not as risky as standing in a puddle touching the body of a car, which is far lower impedance and puts the voltage across the heart.
18:00 to 21:30 explains why there is still a need:So, my view is that as long as there is a proven and reliable earth at the consumer unit there shouldn't be any need for PEN protection.
18:00 to 21:30 explains why there is still a need: