The point where I want to install my wall connector is at least 75 ft away from panel and has to run outside the home along the walls. I am thinking 80-85. I got the 4/3 wire THHN/THWN-2. Ground is #8. Will that wire support 48 amps given the long run? Can I use 60Amp Breaker or Would it be 50Amp breaker?
The cable is not color coded but numbered for conductors 1/2/3. How does it work?
Also I just got the wall connector. 1457768-02-G. Output is 200-240V~48a. And has the SSID. Is that Gen 3 wall connector?
Thank you for help
The cable is not color coded but numbered for conductors 1/2/3. How does it work?
Also I just got the wall connector. 1457768-02-G. Output is 200-240V~48a. And has the SSID. Is that Gen 3 wall connector?
Thank you for help