Thanks5 separate power circuits seems over the top. May be able to consolidate some of those and give you some space in the enclosure.
Consider a garage sub board in case you are going to also add solar
Dont you mean install combined circuit/earth leakage breakers?Two things you should get done when the electrician visits, get a Surge Protection Device (SPD) installed and also just for a safety point of view, install circuit breakers.
Oh and that exposed wiring underneath, that shouldn't be exposed like that.
But yeah, the charger should be a easy install. Just think if you want to do solar or a house battery at home in the future as that may influence your choices of if you want maybe just a single phase installed instead on a circuit not connected to the battery.
5 power circuits is hardly any. My garage has 5! Agree in parramaniacs case a sub-board seems like the right way forward5 separate power circuits seems over the top. May be able to consolidate some of those and give you some space in the enclosure.
Consider a garage sub board in case you are going to also add solar
5 circuits or 5 GPO's?5 power circuits is hardly any. My garage has 5
Actually he has an 80 amp 3 phase main switch so he has 80 amps per phase, don't know what the 20 amp 3 phase circuit breaker is for as it is not marked, but you should have plenty of spare capacity, though it probably wouldn't hurt to do a maximum demand calculation (I could do that for you if you give me enough information), so it comes down to how far you travel each day and how much you are willing to spend to install a chargerWell you have 3phase power So that's good. Looks like you have 20 per phase.
Can't be you would trip it every time you used the AC which is on a single phase 32 amp breakerso the brown one would be the MCB?
Yeah, I didn't look too closely at that. 7kW electrical is a beast of a A/C unit though!Can't be you would trip it every time you used the AC which is on a single phase 32 amp breaker
7kw isn’t that big for A/CYeah, I didn't look too closely at that. 7kW electrical is a beast of a A/C unit though!
The quoted capacity of an A/C is the cooling/heating capacity, not the electrical draw.7kw isn’t that big for A/C
Still doesn’t seem that bigThe quoted capacity of an A/C is the cooling/heating capacity, not the electrical draw.
Daikin's biggest single-phase ducted unit, "15.5kW" has an electrical draw of 5kW.
5 power circuits is hardly any. My garage has 5!
100sqm, and yes correct, dedicated loads to various pieces of equipment, specifically two tesla. 1 for general power 10A, one for a single 15A piece of equipment, and 1 for the backup circuit that does the doors and locks. Actually its more than 5, forgot the aircon(2), pool heat pump (1) and hydronic floor heating (1)Either your garage comprises multiple rooms with 60 GPOs and a total floor area over 400 sq m, which would be an unusual garage, or you have some specialised dedicated loads which under wiring rules require separate circuits.