Vines
Nope, they come with a built in locking hasp on the powerwall switch now.No blade disconnect for each powerwall?
Your service disconnect is inside the combo panel, on the exterior wall hopefully. This cuts grid power to the home.
The Main breaker is to make the panel compliant with 240.21, so that all sources of power don't overload the (assumed 125A) bus and wiring of the existing panel.
2020 NEC 706.15 requires that the Powerwall circuit be all of the following
1. Readily accessible
2. Within sight of the ESS or if impractical as close as practicable and there are marking requirements.
3. Lockable in the open position
4. For 1 and 2-family dwellings, a disconnecting means or its remote control shall be outside and readily;y accessible.
My take is that line is a mistake and doesn't belong in the diagram.
As to the OP, I haven't reviewed the whole thread, but my first reaction is that Tesla may just be avoiding garage installs because in some jurisdictions they had problems with them. I.e. they may only want to do fast and easy installs, and so they may not want to take the time and effort to determine the details of what would be required to do a garage install in your jurisdiction, nor to trust that you have correctly done that work.
Tesla wants to keep installs easy and they aren't setup to go much out of the box and risk having to re-do a bunch of work at final inspection.
Whatttt I need to see a pic of this cool disconnect
There was an internal process change for projects in California that simply prohibits this. While I am not certain on the "why", all of our operations centers throughout California have now moved to only accommodating interior Powerwall installations for detached garages.
Its not a disconnect. Its a small locking hasp on the powerwall switch
This is part of the same discussion thread you already have here, which is why your post was moved into this thread. Its the answer to your thread question, actually, as to "what is preventing this install".
I don't know if this helps, but I think about risk a great deal. (Professionally)@Vines, have you heard anything about Tesla recently "officially" starting to refuse interior PW installations in attached garages "throughout California"?
See where I quote my Tesla advisor in my earlier comment.
Apparently, interior installs in detached garages are still possible... though it would seem to me that, in general, such installs would be potentially way more complex than attached garages (what, with underground conduit runs possibly needed, etc.).
As far as I know, both situations have all the same requirements per the CFC, with the single exception that sprinklers and/or heat detectors are not required in a detached garage. (Am I correct?)
I can't speak for Tesla, or AHJ, but outside installation and installations in detached garages puts the energy storage devices outside of the inhabited envelope of the home. I can imagine some risk assessor sitting at a table with Tesla saying "Why install Powerwalls inside the home or in an inside garage? What is the upside to the added risk?"
Many (most?) interior garages have living spaces over them, often bedrooms. That is high risk for something like eight hours a day.
But it may also be as simple as interior installs take an extra 49 hours of engineering and compliance time, making them uneconomic.
Regardless, Tesla has decided not to do them.
Thanks.
This might also explain the (apparent) cageyness of my advisor. I mean, how would it look insisting a customer must install right outside the kids’ bedroom window (my case) while at the same time explaining the garage is off-limits because of “the risk” (which he hasn’t said; I’m just extrapolating from your comment).
So…. instead it’s all kinda mysterious, and referred to vaguely as a “process change”.
Here’s the document vines shared before about the indoor installation for Woodside. As someone who hates reading, I can understand why a battery installer would just say ****it, we’re installing outdoors.
That doc just seems to be a restatement of the current fire code. It is something more?
It’s got a lot of words and pictures? Don’t have to worry about these words and pictures if you install outdoors. Also keeps your Porsche from hitting a bollard.