It sometimes does feel like some of these sites could use some magic to get them finished.The most recent incantation of this
Haven't seen too much information on the version 3 charger but a new one by me in the Buffalo area (Cheektowaga Supercharger on Plugshare) prompted this email to a friend recently:
Just for a bit of background, Tesla chargers (typically in parking lots) work by getting the VIN of the Tesla charging, and then bill the owner's credit card on file, prior to energizing.
The model used for the first 7 years were 12 '10 kw' car chargers (same as used in the 2013 MODEL S sedan), giving an optimistic 120 kw to charge the car. These were put in 3R rack cabinets along with glycol coolers (as would be used in the car), and provide the rated power at 250 volts and above. Since here, they ran on 277 volts they were used at full power - but a typical installation (at Eastern Hills mall in Clarence) of 8 parking spots would be run by 4 of these rack cabinets - hence they were numbered 1A,1B..... etc on to 4B. To get maximum power, cars would arrive and park somewhere where they were the only car of the same # (the mate parking spot preferably being empty) so that way their cars wouldn't have to 'share' the 120 kw charger with another car.
The most recent incantation of this (so called 'version 3' - I don't know what v2 was), has a much larger convection cooled block (about 3 times the size of the old fan cooled rack cabinets) with the output going to 4 parking spots - in other words, this Cheektowaga location (only a few miles from Eastern Hills) in the Panara Bread parking lot across from Galleria is also 8 stalls but in this case the labeling is 1A, 1B, 1C, 1D for the first charger up to the last parking spot being 2D, with only 2 charger blocks instead of the 4 rack cabinets as at Clarence. So here, a Model 3 vehicle (currently the only Tesla that can go at 250 kw (for 5 minutes) ) would optimally have the other 3 parking spots vacant as to get the full power from the charger for itself.
I took pictures, but they are too large for YAHOO to accept the upload. Incidentally, this was a very low cost installation. Gone is the typical Square-D 3 bay wide QED-2 switchgear (Hollywood Theatre had a ONE-Bay QED-2 to show you how massive 3 must be), and just have 2 - 600 amp mains in separate 3R breaker enclosures - somewhat larger (about 5X) than the one on the back of your house. Each fed (no doubt) by 3- 2-1/2" SCHED 80 pipes with 4-4/0 AL XHHW inside. These are mounted on unistrut with 6 plastic 2-1/2" pvc80 plus expansion sliders going into the ground (3 in, 3 out to the huge charger block, and then the whole thing duplicated. In other words there is no overall main. Just 2 cheap 600 A breakers, in separate enclosures each going to its individual charger block, and then out to 1-4 or 5-8 car charging stalls. Revenue metering is handled by an ESTER type 9S meter (meter multiplier 750 - Nyseg does *NOT* put 277 on the meter (unlike National Grid)- , but only 110.8 volts as inside the 750 kva (coincidence) pad transformer (which the revenue meter is bolted to) are 3 - 2.5:1 voltage transformers and 3- 1500:5 current transformers so 2.5 * 300 = 750 hence the meter multiplier. Both Nyseg and NG use 'high voltage drop' 5.87% impedance transformers that sacrifice tight voltage regulation for minimal fault current available. In this case a 750 kva pad has a full load current rating of 902.5 amperes, and a fault current of a leisurely 15,478 amperes. So, the cheap 600 ampere mains (one of two in this case) only have to have an 18,000 ampere interrupting rating. There is a 3rd 'single phase' 277/480 volt 30 ampere service running to a 3R - Square D double pole 30 amp safety switch which goes to a 'tesla box' which presumably handles the cell-phone call to the data base, and (I'm guessing here) can remote trip the 2 main breakers 'over the phone' should somebody report a fire or explosion. The 3R enclosures for the 600 amp breakers are left unlocked, so this is the FIRST Tesla supercharger installation I've ever seen world-wide that had a 'readily accessible disconnect' - something NEC has ALWAYS required for over 60 amperes or over 150 volts to ground. In Norway, a Tesla Model S burned down to absolutely nothing when a defective car could not be shut down from charging.... None of the supercharger installations had so much as an emergency stop button, something ALL GAS STATIONS have had for decades. Since the car is aluminum, it all goes up in flames once you get it hot enough.
So curiously, this is the first Supercharger installation ever that I've heard about where the Inspector hasn't had to have been bribed.
Here's the charger ratings:
Continuous AC rating : 350 kva @ 480 vAC.
Input: 360-528 vac 3ph (allows anything from 380 in europe to 480 plus 10% in the states)
430 amperes maximum continuous rating, (my interpolated current draw is 421 amperes at 480 volts for 350 kva), however the output from the pad transformer will be around 452 volts due to the 5.87% impedance drop - I don't know if the primary 7200Y/12470 is 'high' in that area or not. Its close but not the same as NG's 13,200 volts.
Individual PORT output availability: (1 of 4): 250 kw maximum per port, 0-500 VDC, 631 amperes max (250 kw interpolated by me would be 396 volts).
Nope. The charger sees "Supercharge Enabled" and supercharges. The car reports the energy used to Tesla, and the amount is added to your bill. No credit card is billed prior to energizing.Just for a bit of background, Tesla chargers (typically in parking lots) work by getting the VIN of the Tesla charging, and then bill the owner's credit card on file, prior to energizing.
Not necessary with v3 chargers. The limit with v3 chargers is the size of the transformer. Even at locations without the transformer capacity to deliver 1000 kWh, charging won't be restricted unless four cars show up at exactly the same moment at very low states of charge.So here, a Model 3 vehicle (currently the only Tesla that can go at 250 kw (for 5 minutes) ) would optimally have the other 3 parking spots vacant as to get the full power from the charger for itself.
That's a serious accusation. You're claiming Tesla has bribed inspectors in every state of the USA?So curiously, this is the first Supercharger installation ever that I've heard about where the Inspector hasn't had to have been bribed.
We noticed.(I'm guessing here)
Except HawaiiThat's a serious accusation. You're claiming Tesla has bribed inspectors in every state of the USA?
and Alaska.Except Hawaii
Nope. The charger sees "Supercharge Enabled" and supercharges. The car reports the energy used to Tesla, and the amount is added to your bill. No credit card is billed prior to energizing.
Not necessary with v3 chargers. The limit with v3 chargers is the size of the transformer. Even at locations without the transformer capacity to deliver 1000 kWh, charging won't be restricted unless four cars show up at exactly the same moment at very low states of charge.
That's a serious accusation. You're claiming Tesla has bribed inspectors in every state of the USA?
So I am very curious to learn the limitations of the V3 chargers. Bill's post is helpful in understanding what they might be. Are we saying that a single cabinet can handle four cars at 250kW simultaneously? A full megawatt in one cabinet? I highly doubt it. More likely than the transformer being the limit (since they are likely 1.5 or 2.5 MVA) is that the feed conductors from the switchgear can't feed that and likely the rectifiers in the V3 supercharger can't do it either (or its cooling). The V3 superchargers probably have some limit just like V2, but it is so much higher that Tesla figures it will virtually never be hit due to the connected cars being at the wrong state of charge, cold battery, etc...
Awesome writeup!
I assume you are a power systems engineer?
FWIW, I think V1 vs V2 superchargers are slightly different. I think V1 was based around the tech that drove the original 40kw chargers in the original model S, and the V2 was based on the newer chargers in the S and X current models. One big difference is that the newer ones would not handle the higher voltages (they would error out) and so Tesla had to go back and retrofit a bunch of “buck” transformers into a bunch of supercharging stations since the utility voltage might vary at times. They also stopped supporting 277v to Wall Connectors because of this.
I am told that Model 3’s chargers have no such issue with 277v +10%.
I kind of want to put a 277v Wall Connector at work just for funsies...
Oh that's just silly. While I don't know precisely the mechanism for billing the customer, there is communication with a Tesla database that provides billing information. The more serious error on my part is what the 'TESLA BOX' does on the 'Service Entrance Unistrut'. Apparently if the car 'handles' the billing, then the former is strictly for management of the charger boxes.Nope. The charger sees "Supercharge Enabled" and supercharges. The car reports the energy used to Tesla, and the amount is added to your bill. No credit card is billed prior to energizing.
Not necessary with v3 chargers. The limit with v3 chargers is the size of the transformer. Even at locations without the transformer capacity to deliver 1000 kWh, charging won't be restricted unless four cars show up at exactly the same moment at very low states of charge.
That's a serious accusation. You're claiming Tesla has bribed inspectors in every state of the USA?
We noticed.
Haven't seen too much information on the version 3 charger but a new one by me in the Buffalo area (Cheektowaga Supercharger on Plugshare) prompted this email to a friend.
Smathew said:
"....Not necessary with v3 chargers. The limit with v3 chargers is the size of the transformer. Even at locations without the transformer capacity to deliver 1000 kWh, charging won't be restricted unless four cars show up at exactly the same moment at very low states of charge...".
Oh boy, another self-appointed Big Expert.
Chief: 1000 kw at 480 volts is around 1,204 amperes, and that assumes the fantasy of 100% efficiency and 100% Power factor.
Assuming the efficiency is slightly less than 100%, 1300 amperes on a 600 ampere circuit breaker (especially an '80% rated' one) will tend to nuisance trip it.
A 600 ampere circuit breaker is just ducky for a Continuous Load where the maximum continuous load PER THE TESLA NAMEPLATE is 350 kva; around 422 amperes at 480 volts, or 447 amperes at the more likely expected 452 volts, as I explained in my original letter to my friend.
Oh, ok great! Your explanation explained why they first allowed 277, and then, didn't!
As regards the charger ultimate draw, the Nameplate info on the Charger clearly states it is rated for 350 kva @ 480 volts.
Since the nameplate says the allowable input voltage is 360-528 volts it looks like a 'clean sheet' design and doesn't bother with 240-277 any longer. In this 8 stall installation - there were 2 - 600 ampere breakers (1 per charger block), with no overall main - the Breakers themselves being a 'multi-main'. Very low cost. This particular Utility (New York State Electric and Gas) allows all kinds of customer friendly designs (in this case 3 service disconnects: 2 - 3 pole 600 amp breakers, and 1 - 2 pole 30 amp fusible switch).
i mean THEY ARE RIGHT NEXT TO EACH OTHER!!and Alaska.
Forgot about both of them.
Here is a past thread I started on 277v specifically: Info from Tesla - 277v feed to Wall Connector (HPWC) - Which Cars Support It
FWIW, I am pretty sure each rectifier module in the new V3 superchargers is still 277v since they have a neutral in all the feed conduits from the main switchgear.
Check out the nameplate one the new one at Vancouver Mall in Washington:
I have not seen anyone else talk about how fascinating the DC Input / Output section is! Clearly to me this is intended either for multiple cabinets to load share with each other (if one has four cars all demanding super high charge rates), or perhaps more likely it is intended for Tesla Batteries (Which could both help with the surge load need for hungry cars and also help reduce demand charges, time shift energy charges, make better use of renewables, etc...). Up to 640 amps and 1000 volts!!!
I can't wait to try one!
View attachment 520175