I have a subpanel in the garage. it is powered by 4 #10 gauge wires from main panel. The distance is about 80 feet. The breaker size is 30 A from the main. Two questions:
1: Is installing a 30 A capable socket (like 6-30 or 14-30) on a subpanel with 30A breaker from main violating any code ?
2: Will 24A charging trip the breaker ? the rest of the electronics on that subpanel is less than 200 watts. I thought it will be OK, just want to verify