I have a question about grounding, from reading the manual from my generator do I have to ground the generator if I run it from inside the bed of the truck.
Since there's no Superchargers along my route, I'm trying to make it to the lake and back home pulling my boat.
I can make it both ways but I have to drive one way 55mph and home at 50mph to make it.
I'm wanted to try and get 25 miles or so out of the generator while the truck sits in the boat parking for 4-5hrs. This way I can drive 65mph both ways.
By reading this below from the manual, will I be able to charge with the generator in the bed of the truck, or does it have to be on the ground. I'm also running a small fan facing the generator just to help cool the generator in the 110-115 degree temps.
Grounding
Your generator must be properly connected to an appropriate
ground to help prevent electric shock.
WARNING
Failure to properly ground the generator can result in electric
shock.
A ground terminal connected to the panel of the generator has
been provided (see Controls and Features for terminal location).
For remote grounding, connect a length of heavy gauge
(12 AWG minimum) copper wire between the generator ground
terminal and a copper rod driven into the ground. We strongly
recommend that you consult with a qualified electrician to ensure
compliance with local electrical codes.
Neutral Floating*
– Neutral circuit IS NOT electrically connected to the frame/
ground of the generator.
– The generator (stator winding) is isolated from the frame and
from the AC receptacle ground pin.
– Electrical devices that require a grounded receptacle pin
connection will not function if the receptacle ground pin is not
functional.
Neutral Bonded to Frame*
– Neutral circuit IS electrically connected to the frame/ground of
the generator.
– The generator system ground connects lower frame crossmember
below the alternator. The system ground is connected
to the AC neutral wire.
Since there's no Superchargers along my route, I'm trying to make it to the lake and back home pulling my boat.
I can make it both ways but I have to drive one way 55mph and home at 50mph to make it.
I'm wanted to try and get 25 miles or so out of the generator while the truck sits in the boat parking for 4-5hrs. This way I can drive 65mph both ways.
By reading this below from the manual, will I be able to charge with the generator in the bed of the truck, or does it have to be on the ground. I'm also running a small fan facing the generator just to help cool the generator in the 110-115 degree temps.
Grounding
Your generator must be properly connected to an appropriate
ground to help prevent electric shock.
WARNING
Failure to properly ground the generator can result in electric
shock.
A ground terminal connected to the panel of the generator has
been provided (see Controls and Features for terminal location).
For remote grounding, connect a length of heavy gauge
(12 AWG minimum) copper wire between the generator ground
terminal and a copper rod driven into the ground. We strongly
recommend that you consult with a qualified electrician to ensure
compliance with local electrical codes.
Neutral Floating*
– Neutral circuit IS NOT electrically connected to the frame/
ground of the generator.
– The generator (stator winding) is isolated from the frame and
from the AC receptacle ground pin.
– Electrical devices that require a grounded receptacle pin
connection will not function if the receptacle ground pin is not
functional.
Neutral Bonded to Frame*
– Neutral circuit IS electrically connected to the frame/ground of
the generator.
– The generator system ground connects lower frame crossmember
below the alternator. The system ground is connected
to the AC neutral wire.