Can you post to confirm the PW+ specs (max continuous current, overcurrent protection, etc.)?They installed the new pw+ And solar last Friday
You can install our site as a web app on your iOS device by utilizing the Add to Home Screen feature in Safari. Please see this thread for more details on this.
Note: This feature may not be available in some browsers.
Can you post to confirm the PW+ specs (max continuous current, overcurrent protection, etc.)?They installed the new pw+ And solar last Friday
This is what they installed. As far as specs, I didn’t get much info and know only what others have posted here. All the paperwork I got from Tesla was for the old pw2. The installers said this was the first pw+ they installed. I’m in Fort Worth, TX.Can you post to confirm the PW+ specs (max continuous current, overcurrent protection, etc.)?
This is what they installed. As far as specs, I didn’t get much info and know only what others have posted here. All the paperwork I got from Tesla was for the old pw2. The installers said this was the first pw+ they installed. I’m in Fort Worth, TX.
With the adapter ring on the meter, or with a separate gateway box between the meter and the main panel? Still waiting to see an instance of that adapter ring in real life.They installed the new pw+ And solar last Friday
Thanks for the photos. Can you show a closeup of the adapter ring, perhaps from the side so you don't need to black out the meter face? If there is any label on the ring, that would be interesting to see.This is what they installed. As far as specs, I didn’t get much info and know only what others have posted here. All the paperwork I got from Tesla was for the old pw2. The installers said this was the first pw+ they installed. I’m in Fort Worth, TX.
Given that, the meter adapter wiring may still be control only for a relay, rather than power; the disconnect would just be used as a convenient wiring compartment. I.e. the wiring would be:They added breaker to the main panel and they said that was the battery breaker.
Good hypothesis, but I don't see a conduit from the disconnect to the main panel. I presume the disconnect is new for this installation since there would not have been a need for it without local generation.Given that, the meter adapter wiring may still be control only for a relay, rather than power; the disconnect would just be used as a convenient wiring compartment. I.e. the wiring would be:
Meter - Control Wiring Straight Through Disconnect - PW+ - Power Wiring Through Disconnect Terminals - Main Panel
If you look at the geometry, it is plausibly back to back with the disconnect.Good hypothesis, but I don't see a conduit from the disconnect to the main panel.
If you look at the geometry, it is plausibly back to back with the disconnect.
Cheers, Wayne
Generator transfer switches exist as meter adapters, but I'm not aware of anyone else putting a Microgrid Interconnect Device into a meter adapter.And it's interesting that the meter adapter is a Tesla product, so I guess no electrical equipment manufacturer came up with this idea before.
They do allow them for solar: https://www.pge.com/pge_global/comm...tion/greenbook-manual-online/TD-7001B-007.pdfFWIW: A number of IOU do not allow meter adapters. I believe PG&E is one of them, based on prior conversations with them for a generator adapter.
I would be interested to hear their justification for disallowing a UL listed product applied in the intended manner.FWIW: A number of IOU do not allow meter adapters. I believe PG&E is one of them, based on prior conversations with them for a generator adapter.
All the best,
BG