Unsure what you were expecting. Nameplate rating is over the operating temperature range. Elon Tweeted about a power boost in a reduced temperature band around 30C. No reason for them to change the placard and open up liability in case they need to dial it back.
Elon referring to reserve capacity:
Elon talking the HW limits:
A 30 Amp breaker trip will allow 2x current (14.4kW) for 10 seconds. It will also allow 10kW for 30 seconds. The surge is to allow AC compressors to start, not to run high continuous load appliances. For reference, check the LRA Amp vs circuit breaker size on an air conditioner.
View attachment 778818