Vines
Active Member
There are several non interconnected ones available for conditioned garages (135F max) The one specified by Wayne is allowed by SCC fire, for a conditioned space.
If your garage is not conditioned, and the construction is such that the interior temperature could reach 100 degrees (not in a basement or with living space above it), then you would need a heat detector rated for 194F degrees. So far I cannot find any non-interconnected versions rated for 194F degrees. Our only solution is to install an interconnected system.
I cannot speak to the others, but the Nest is not listed as a heat detector, though it can sense heat. SCC fire specifically said no to the Nest and I talked to the tech support at Nest trying to convince them to list it. Happy to hear the other interpretations of the code, but the one that matters is the Fire Marshall's. When the language required interconnected heat detectors it was even worse, at least they don't need to be interconnected now.
As for the update from Wayne, its all accurate but a couple items to add:
Engraved plaques are pretty universally accepted per the NEC, made with special plastic designed for laser engraving. They have never required aluminum backed signs to my knowledge.
I don't know of any cell on the market today that would pass the 9540A test with the "For use in residential dwelling units" Unless the cell is absolutely impossible to send into thermal runaway, through any means of destruction (heading, crushing, puncturing etc.) Literally the test is that if the cell cannot be sent into any measured thermal run away then it will pass, pretty high bar.
R327.4 If you are within the building envelope (batteries under or in a living space) its 5/8" Type X sheetrock required, and a fire rated door.
R327.3 To get closer than 3' spacing requires 9540A testing, its a whole series of tests.
If your garage is not conditioned, and the construction is such that the interior temperature could reach 100 degrees (not in a basement or with living space above it), then you would need a heat detector rated for 194F degrees. So far I cannot find any non-interconnected versions rated for 194F degrees. Our only solution is to install an interconnected system.
I cannot speak to the others, but the Nest is not listed as a heat detector, though it can sense heat. SCC fire specifically said no to the Nest and I talked to the tech support at Nest trying to convince them to list it. Happy to hear the other interpretations of the code, but the one that matters is the Fire Marshall's. When the language required interconnected heat detectors it was even worse, at least they don't need to be interconnected now.
As for the update from Wayne, its all accurate but a couple items to add:
Engraved plaques are pretty universally accepted per the NEC, made with special plastic designed for laser engraving. They have never required aluminum backed signs to my knowledge.
I don't know of any cell on the market today that would pass the 9540A test with the "For use in residential dwelling units" Unless the cell is absolutely impossible to send into thermal runaway, through any means of destruction (heading, crushing, puncturing etc.) Literally the test is that if the cell cannot be sent into any measured thermal run away then it will pass, pretty high bar.
R327.4 If you are within the building envelope (batteries under or in a living space) its 5/8" Type X sheetrock required, and a fire rated door.
R327.3 To get closer than 3' spacing requires 9540A testing, its a whole series of tests.