I may be misunderstanding the question, but the Gateway must be fed by a breaker no larger than 200A. That will protect it from overload. In certain conditions it may be possible to power more than 200A of loads due to adding grid and local generation, but those don't pass through the Gateway switch from the grid, which is where the 200A breaker should be.To be clear, adding a non backup panel and running a feeder cable from gateway to the generation disconnect and taps to the house panels is acceptable by inspectors even though you have the possibility of overloading the gateway?
A non-backup panel is by definition, not fed by the Gateway. It is fed from your utility meter before the 200A branch that goes to the Gateway. Therefore, energy cannot flow back to a non-backup panel from the batteries and solar while the grid is down. The Gateway switch is a hard demarcation line for what is grid-only and what is backed up.