I want my 2 powerwalls to charge to 100% but only if there is excess solar production.
If my home usage exceeds the solar production I want the excess to come from the grid.
Is this possible?
Example: In Self-Powered setting with 25% reserve
4.3 kW Solar
3.3 kW Home
1.0 kW going to the PW
If my AC cycles on then I get
4.3 kW Solar
6.8 kW Home
2.5 kW from PW to home
Advanced Mode (balanced) with 25% reserve & Backup Only have the same behavior
100% of the Home load comes from Grid
100% of the Solar production goes to Powerwall
I'm testing this on a Saturday (all off-peak) if that matters.
Thanks!