Hmmm... When I installed my 14-50R I had a GFCI breaker identical to what's in this Milbank configuration, and 90% of the time the breaker would trip with the UMC during the blue flash phase starting charging. I noticed that the UMC specs on the back mention 18mA trip leakage while my GFCI breaker was 5mA trip leveled. I'm curious if other people with UMC's have GFCI's on their 14-50's and if they are successful in using them. I've switched to a normal, non-GFCI breaker, but I'm not comfortable with that. I've seen that there are equipment protection breakers which trip at 10mA and 30mA which would give a person a shock but probably not fatal and still protect "equipment." I figure if the UMC trips at 18mA, a 30mA breaker shouldn't trip first. Maybe I have a bad UMC?