Looks like that is correct. The Powerwalls are designed as such that they never export to the grid. So they would not need to be accounted for in the main bus 120% rule for back feeding. So it looks like as of now with 60amp max of solar running through the Enphase aggregator I can keep the 200 amp service disconnect.