Lithium-ion battery fires do not depend upon external oxygen to burn. The materials inside the cell provide both fuel and oxidizer.I wonder if this blanket can starve a powerwall fire and it eventually goes out if left on for hours.
You can install our site as a web app on your iOS device by utilizing the Add to Home Screen feature in Safari. Please see this thread for more details on this.
Note: This feature may not be available in some browsers.
Lithium-ion battery fires do not depend upon external oxygen to burn. The materials inside the cell provide both fuel and oxidizer.I wonder if this blanket can starve a powerwall fire and it eventually goes out if left on for hours.
Technically, since it is UL listed for stacking it is a single unit in the eyes of the code. Agree most AHJs consider all electrical equipment to require access while energized. Transformers used to be an exception 10-20 years ago, but not today in most places.I am speaking of a general NEC requirement 110.26. The answer to your question depends on the AHJ. In my opinion the PW switch on the side means it is likely to need someone to operate it while energized. This switch is needed to commission the system, change the settings or reset the system.
I am curious to hear others opinions on this item, since technically a stack of 3 powerwalls violates working clearance for the rear most unit.
Great answer, I'm going to use that one!Technically, since it is UL listed for stacking it is a single unit in the eyes of the code. Agree most AHJs consider all electrical equipment to require access while energized. Transformers used to be an exception 10-20 years ago, but not today in most places.
I also found the code citation for that:Great answer, I'm going to use that one!
the installation instructions specify the clearance needed on all sides. It's mostly for thermal management ventilation.Given the only servicable part of a powerwall is the switch on the side, would a single powerwall install with say just 12" of front clearance and 12" of right-side clearance inside a fire closet be sufficient? i.e. enough that someone can easily operate the switch.
I would give it much more space, as there are replaceable parts that are only accessed from either side, like 3 feet either side. The tech needs to be able to get to the sides as well. You don't want a tech having to take the Powerwall off the wall just to service something small.Given the only servicable part of a powerwall is the switch on the side, would a single powerwall install with say just 12" of front clearance and 12" of right-side clearance inside a fire closet be sufficient? i.e. enough that someone can easily operate the switch.
Minimum clearance from left side (air intake) | 2 in (50 mm) |
Minimum clearance from right side (air exhaust) | 6 in (150 mm) |
Minimum clearance above single Powerwall | 2 in (50 mm) |
Minimum clearance above side-by-side Powerwalls | 12 in (300 mm) |
Minimum clearance between side-by-side Powerwalls | 10 in (250 mm) |
I think that you are right to be concerned about ventilation. Each Powerwall throws off 100W or so in idle, so heat will build up quickly in a small space. BUT, you want to vent this to the outside directly, so that any flames go outside rather than across your basement, which is what the AHJ is concerned about, right?Thanks @miimura and @BGbreeder for replies! FWIW @miimura the install manual available from Telsa (page 41) gives very small clearances:
Minimum clearance from left side (air intake) 2 in (50 mm) Minimum clearance from right side (air exhaust) 6 in (150 mm) Minimum clearance above single Powerwall 2 in (50 mm) Minimum clearance above side-by-side Powerwalls 12 in (300 mm) Minimum clearance between side-by-side Powerwalls 10 in (250 mm)
Nothing about front though. Thanks @BGbreeder, I didn't know how common such servicing is but assumed most of that would be done via the front taking off a front panel and that 12" on each side would likely be sufficient. Wouldn't be too hard to give more side clearance.
Main thing I really don't know is how much front clearance is required and whether a standard (32"?) fire door in front of the Powerwall would be adequate for whatever clearance is required. Either way, the ventilation definitely seems like an issue and not something I see specified at all in the installation manual. Quite the opposite it seems like it expects to be installed somewhere open with air flow, rather than somewhere fire sealed like the AHJ is requesting.