Thanks, I'm beginning to understand it nowThe ampacity charts clearly state that NM-B (Romex) in 6 gauge is rated for a maximum of 55 amps. Other types of wire, in 6 gauge, depending on the maximum temperature for the application may be rated for higher amperage.
Cerrowire Resources - Ampacity Charts
For 6 gauge,
Romex - NM-B is classed as a 60 degC conductor, so is only rated to 55amps
Single conductor - THWN is a 65 degC conductor, so is rated to 65 amps, because it's heat resistant
Single conductor - THHN is a 90 degC conductor, so is rated to 75 amps, because it's a High Heat conductor
and I think the last two are stranded. Interestingly, stranded was a requirement when I installed the mini-split
So if I run some THHN in conduit, do I need to use blue and yellow for the energized conductors?
This is interesting stuff