Found an electrician who will charge me for labor only if I provide them with the materials and for a good rate. Looks like I will be running 85-100 ft wire. What all items are needed to have it install? I will pick it up at Home Depot. Thanks!
You can install our site as a web app on your iOS device by utilizing the Add to Home Screen feature in Safari. Please see this thread for more details on this.
Note: This feature may not be available in some browsers.
You need a 50-amp double pole breaker that matches your box. Look in your box and see what brand breakers are in there already. Then go to Lowes or HD to buy the same brand, but be sure it's a 50-amp double pole.Found an electrician who will charge me for labor only if I provide them with the materials and for a good rate. Looks like I will be running 85-100 ft wire. What all items are needed to have it install? I will pick it up at Home Depot. Thanks!
He needs 4/3 wire because of the length of his run. That will cost around $450.You need a 50-amp double pole breaker that matches your box. Look in your box and see what brand breakers are in there already. Then go to Lowes or HD to buy the same brand, but be sure it's a 50-amp double pole.
You also need a 14-50 exterior box. I bought an Eaton at Lowes. Someone else mentioned the wiring already. You'll also need 1" conduit with water-tight connectors to run the wiring thru.
I bought my own Eaton NEMA 14-50 box, with $10 breaker, and conduit, and 8' of 6/3 wire, for $75, all bought at Lowes. Your wiring alone will probably cost over $300. So, altogether under $400.
Okay, I thought you went up a size if over 100ft, he said 85ft to 100ft.He needs 4/3 wire because of the length of his run. That will cost around $450.
He needs 4/3 wire because of the length of his run. That will cost around $450.
No.
If he runs 6 AWG copper wire and actually pulled a FULL 50 amps (not possible for an EVSE since they are limited to 40 amps on a 50a circuit as it is a continuous load, and the UMC Gen 2 is only 32 amps!) and if we use a horribly conservative voltage drop allowance of 2% (NEC recommends a max of 3%, but then also not more than 3% on feeders, with a combined total loss of 5%, so hence the being super conservative at 2%), then he still can still run it 108 feet!
If we back that down to 40 amps max draw we get 135 feet. If we up it to 3% allowed loss but back to 50 amps we get 162 feet.
Now these NEC recommendations are just that - recommendations - nearly everything in NEC is rules, but there are not rules for voltage drop surprisingly enough.
So while it is not optimal, I think that in some situations it is OK to have pretty hefty voltage drops for EV charging. Unlike some motors that work harder when their voltage is low, EV's just charge a little slower. The onboard rectifier can handle 100-240v at least, so not that big a deal if you have a lot of drop. The only trick is to avoid Tesla's throttling due to it thinking there is a wiring issue. It looks at the voltage before charging and then watches it after it starts charging. If it drops too much it assumes there is a wiring issue and will slow down or stop the charge.
I have seen wire upsizing pushed around here on the forums in a lot of situations where I just don't think it is necessary. Dealing with 4 AWG is kind of a pain compared to 6 AWG (which is still a pain).
If you upsize you can be prepared for a HCWC should you want one or get a free one for referrals. Also ready if you get a second Tesla and can load share, I would think this will be supported with other brands of charger later too.
3gauge THHN is $1.02 a foot at Home Depot and an 8 gauge ground $.56 a foot. It is early maybe my math is off but that is $260 then you need conduit. This will run the circuit capable of feeding a 90amp HCWC and allow you to charge even a LR M3 50% faster than the UMC.
You could do a 6-50 adapter which is 50amp 240 and save running a 4th wire if you want to put off HCWC purchase and just use a 50amp breaker for now. The adapter is cheaper than the 4th wire a 14-50 needs.
Now you should talk to the electrician to see if you have the capacity and if he is going.to gouge you on labor for big wire but know you have options besides bare minimum and that actually materials cost difference is NOT that high.
I am going to get some quotes for a NEMA 14-50 outlet in my garage. I have a 100A panel with 6 open slots(3 on each side). I would like to install the outlet about 6-12 inches from the panel, surface mounted. I bought the NEMA 14-50 outlet(Hubbell HBL9450A) and Hubbell 4" box. So basically I just need the 50A breaker and wire. I was going to leave that up to the electrician. What type/gauge wire would I need?
Got it. 6 AWG copper wire and a compatible 50 A dual pole breaker. Seems pretty easy. 50A breaker and 2 ft of wire is cheap, so cost is all labor. Hopefully the cost will reflect that.