Everyone here hopefully already knows about the wire temp ratings. For example, assuming copper, NM-B (romex) = 60C vs THHW = 75C.
So for a 60A circuit, we can use:
1.
#4 NM-B, or
2.
#6 THHW in conduit
However, one thing folks often overlook is the
ambient temp rating! The NEC ampacity table 310.16 clearly state that the ratings are "Based on Ambient Temperature of 30°C (86°F)". The
expanded NEC table shows the temp correction factors for ambient temperatures other than 30°C (86°F). Be sure to keep these correction factors in mind when deciding on cable!
For example in my case, I have to run 60 feet of cable through the attic from the breaker panel (in the back of the house) to the garage (in the front of the house). 50 ft of it is in the attic. On a hot summer day in CA, the attic will be well over 49C/120F! Even if you run the cable on the exterior of the house, it will be subject to heat and potentially direct sunlight, raising the temperature.
Thus taking the ambient temp correction factors (46–50C/114–122F) in mind,
neither one of the two solutions above work:
1. (#4 NM-B): 70A * 0.58 =
40.6A
2. (#6 THHW): 65A* 0.75 =
48.75A
To make it work, we need to size up:
1. (#1 NM-B): 110A * 0.58 =
63.8A
2. (#4 THHW): 85A * 0.75 =
63.75A
When comparing prices, which one do you think is cheaper? It becomes a no brainer to use #4 THHW in conduit! #1 NM-B will be much more expensive, harder to find, and harder to work with.
Many of you are lucky to have your breaker panel already in the garage, so you don't have to go through a hot attic. But if its anything like my garage, it will still get above 90-100F in the summer (partially insulated garage). Who knows how warm it is inside the walls of a garage. So it would still be a safe bet to use the 36–40C/96–104F correction factor.