SageBrush
REJECT Fascism
Nah.and probably 20-30kwh/day in the summer if this is correct
Use pvwatts
You can install our site as a web app on your iOS device by utilizing the Add to Home Screen feature in Safari. Please see this thread for more details on this.
Note: This feature may not be available in some browsers.
Nah.and probably 20-30kwh/day in the summer if this is correct
i'm in colorado at 5k feet, mostly bright sunny days here. My panels are not all in the exact same direction but close, all my panels are mostly facing south, i have relatively direct exposure to all panels for significant portion of the day. I hit 7.6kw at 10:30am and stayed there till 2:30pm.. Summers will be significantly better as sun is pretty low in the sky right now. I had to increase my home coverage to support >10kW, but if my system is truely limited to 7.6kw due to hardware this seems like a money saving ploy on tesla's part if my solar system can indeed generate >7.6kw for sig. portions of time. Non-tesla installer who installed system at my neighbor said the solar inverter should be sized similar(maybe a little lower) than my true solar capacity. Friends down the street with 8kw tesla system peak at 7.6kw daily. Yes, i understand when my system is running below max capacity my extra solar arrays give me extra power, but i paid for a 12kw system. I have a friend in California that has a 12kw system, he has a 7.6 and a 3.8 inverter. Need to go thru inspection tomorrow, get PTO, but this seems a bit odd to me.No overdrive.... They would need to increase your wiring awg size and breaker size to handle the higher output, if they never did that during install....
Where are you located? All your panels face the same direction and which direction?
Your 7.6 kW inverter will likely never see more than about 7.8 kW. It is constrained by its rating, the wire and breaker size, and cannot "overdrive" beyond 32A for any significant length of time.i'm in colorado at 5k feet, mostly bright sunny days here. My panels are not all in the exact same direction but close, all my panels are mostly facing south, i have relatively direct exposure to all panels for significant portion of the day. I hit 7.6kw at 10:30am and stayed there till 2:30pm.. Summers will be significantly better as sun is pretty low in the sky right now. I had to increase my home coverage to support >10kW, but if my system is truely limited to 7.6kw due to hardware this seems like a money saving ploy on tesla's part if my solar system can indeed generate >7.6kw for sig. portions of time. Non-tesla installer who installed system at my neighbor said the solar inverter should be sized similar(maybe a little lower) than my true solar capacity. Friends down the street with 8kw tesla system peak at 7.6kw daily. Yes, i understand when my system is running below max capacity my extra solar arrays give me extra power, but i paid for a 12kw system. I have a friend in California that has a 12kw system, he has a 7.6 and a 3.8 inverter. Need to go thru inspection tomorrow, get PTO, but this seems a bit odd to me.
i'm in colorado at 5k feet, mostly bright sunny days here. My panels are not all in the exact same direction but close, all my panels are mostly facing south, i have relatively direct exposure to all panels for significant portion of the day. I hit 7.6kw at 10:30am and stayed there till 2:30pm.. Summers will be significantly better as sun is pretty low in the sky right now. I had to increase my home coverage to support >10kW, but if my system is truely limited to 7.6kw due to hardware this seems like a money saving ploy on tesla's part if my solar system can indeed generate >7.6kw for sig. portions of time. Non-tesla installer who installed system at my neighbor said the solar inverter should be sized similar(maybe a little lower) than my true solar capacity. Friends down the street with 8kw tesla system peak at 7.6kw daily. Yes, i understand when my system is running below max capacity my extra solar arrays give me extra power, but i paid for a 12kw system. I have a friend in California that has a 12kw system, he has a 7.6 and a 3.8 inverter. Need to go thru inspection tomorrow, get PTO, but this seems a bit odd to me.
Thanks Vines, a brief conversation with someone at tesla today seems to indicate they likely underestimated my peak solar output. I know other folks that have 12kw arrays have 2 inverters, 7.6 and a 3.8. Not sure how tesla is going to respond.. Will see..Your 7.6 kW inverter will likely never see more than about 7.8 kW. It is constrained by its rating, the wire and breaker size, and cannot "overdrive" beyond 32A for any significant length of time.
The 32A rating is as much as you will ever see, so if the grid is perfectly at 240vac, that is exactly 7.68 kW. If your grid voltage is over or under that then the inverter output will be a bit over or under its rating. In some crazy part of the world with a grid that was just at the upper edge of the UL allowable voltage range, you might see 8.32 kW at 260 vac. I know of no such place, and most likely you are going to get within a few percent of the rated power, which is 7.68kW at 240 volts.
FWIW, I have a 11.9kW system. 3 strings (11, 11, and 12). All are on the same plane/direction. Tesla has me on 2 inverters, the 7.6 and 3.8. I have seen my system peak out at 11.6kW a few times (and even 11.7kW, very rarely) throuhgout the summer (Southeastern PA).Thanks Vines, a brief conversation with someone at tesla today seems to indicate they likely underestimated my peak solar output. I know other folks that have 12kw arrays have 2 inverters, 7.6 and a 3.8. Not sure how tesla is going to respond.. Will see..
Nobody at Tesla underestimated it, they decided it was ok to run a 7.6 kW inverter with 11-12 kW worth of solar roof panels. Especially in the high elevations of Colorado, solar irradiation can be as good as it is in the Bay Area.Thanks Vines, a brief conversation with someone at tesla today seems to indicate they likely underestimated my peak solar output. I know other folks that have 12kw arrays have 2 inverters, 7.6 and a 3.8. Not sure how tesla is going to respond.. Will see..
If this were my installation, I would want to get a fairly good estimation of how much energy is being lost compared to having an additional inverter. That way, I would know if it is worth pursuing the issue with Tesla. Secondly it would, I believe, help in demonstrating to Tesla that the system needs to be improved if that is what the estimate shows.Thanks Vines, a brief conversation with someone at tesla today seems to indicate they likely underestimated my peak solar output. I know other folks that have 12kw arrays have 2 inverters, 7.6 and a 3.8. Not sure how tesla is going to respond.. Will see..
While I generally agree with this approach, the other piece that needs to be addressed is what was contracted. In particular, what (if any) specs were provided that indicated the number/size of inverters and what was the estimate for annual production? It does all get a bit murky, because the contract itself may not list the inverter specifics, and the annual estimate is not a contract guarantee, but my general point would be that Tesla arguably provided what was contracted for if they did not deviate from any inverter specs and if the system meets the estimates provided by Tesla. Put another way, if a solar install hypothetically could generate 25 MWh annually based on the panels but will only generate something like 20 MWh due to the inverters, that is certainly a big loss, but if the customer was told to expect 20 MWh, then they got what they were promised.If this were my installation, I would want to get a fairly good estimation of how much energy is being lost compared to having an additional inverter. That way, I would know if it is worth pursuing the issue with Tesla. Secondly it would, I believe, help in demonstrating to Tesla that the system needs to be improved if that is what the estimate shows.
With that information in hand, one can use PVWatts to get an estimate of annual production. PVWatts tries to take historical weather patterns into account
10-30% less efficient is true. Comparing to Solar Panels at a nearby site with the same array size but are panels instead, I generally lag 20% less efficient comparing non peak times. That array gets max of around 10kw/h so the 7.6 I have currently now is pretty close. I'm probably only clipping maybe at most 5kw on a perfect day. It's very cloudy here in Florida and for the last month of data, there has only been only one day where there's a consistent plateau at 7.6.Nobody at Tesla underestimated it, they decided it was ok to run a 7.6 kW inverter with 11-12 kW worth of solar roof panels. Especially in the high elevations of Colorado, solar irradiation can be as good as it is in the Bay Area.
I'll assume Tesla tells you it's working as intended, based on my rough calculation of energy lost due to the design of the Solar Roof.
Solar roofs are somewhere between 10-30% less efficient than comparable discrete PV modules from what I have gathered so far, so comparing apples to oranges only leads to juice.
10-30% less efficient is true.
That seems to be excessive clipping!!Here's day 1, flat top is 4 hours wide, last week, system hasn't been on since then. This is a normal, representative weather day, since may with exception of sun angle is lower of course. Anyone see this type of clipping as a typical day? An unofficial conversation with a tesla electrician said he'd never seen a discrepecy between solar/inverter as large.. 12.2kw/7.6kw(powerwall plus).. Most of the points above are valid, however i haven't found a single person that experiences this amount of clipping. Seems to be relatively rare, but i'm still looking.
View attachment 712915
That seems to be excessive clipping!!
Goes back to posts many times, does one want to spend more more on inverters for this.Nah... it's fine
View attachment 712962
It looks worse than it is. Annual loss is < 5%. And keep in mind that as solar becomes more prevalent clipping will increasing occur when there's likely to be curtailment anyway so you're losing the least valuable energy.
So how did 11/15 look?so many clouds here in Florida - tried to find the worst "plateau" days.
Any update on overdrive. Am sure thats the first answer we get from tesla. Had similar concern 11.6kw with one powerwall plus. Did someone actually see overdrive? Else what are the resolutions others are getting??Getting the Tesla Solar Roof installed right now. They upsized my system from 7.5kw to 11.6kw (limit for Tier 1 in Florida). I currently only have one Powerwall+ that will be installed. I thought I was going to get two because they promised a free one, but apparently the free one is the one I am already getting.
My question is, will a single inverter inside my sole Powerwall+ handle the a full load? I live in Central Florida so there are definitely days where its sunny and the majority of panels are all south facing with no shading at any time. Is it possible to get another inverter but not another Powerwall+? Or just get another Powerwall+? I just thought of this today, my project took only 1 month from contract to install so this didn't even cross my mind in the last month.
Edit - Apparently the Powerwall+ can kick into Overdrive to 12kw as just responded from my Tesla Advisor. This is done through software. Adding another inverter is not ideal as it will cause energy loss because the inverters themselves consume energy. Anyone have real world examples?
Any update on your resolution by tesla? Am in same boat as you. Told they can overdrive but i asked them to escalate it to design team. Unfortunately the installation is done so not sure what the outcome will be. Fingers crossed.Getting the Tesla Solar Roof installed right now. They upsized my system from 7.5kw to 11.6kw (limit for Tier 1 in Florida). I currently only have one Powerwall+ that will be installed. I thought I was going to get two because they promised a free one, but apparently the free one is the one I am already getting.
My question is, will a single inverter inside my sole Powerwall+ handle the a full load? I live in Central Florida so there are definitely days where its sunny and the majority of panels are all south facing with no shading at any time. Is it possible to get another inverter but not another Powerwall+? Or just get another Powerwall+? I just thought of this today, my project took only 1 month from contract to install so this didn't even cross my mind in the last month.
Edit - Apparently the Powerwall+ can kick into Overdrive to 12kw as just responded from my Tesla Advisor. This is done through software. Adding another inverter is not ideal as it will cause energy loss because the inverters themselves consume energy. Anyone have real world examples?