- Are you still happy with it ? I am planning on buying the 15kW 48V. Wanted to check if that is still a good buy or if there are better option for a split phase 120/240v system
- Yea I'm still happy with the inverter, I wish it curtailed but that isn't too big of a deal. SMA now makes the Sunny Island if you really want an inverter that can curtail, however it's only a 6kW and the peak isn't anywhere near the Sigineer, you'd have to parallel 3 units to get 15kW and triple the cost. SMA now also makes a 350v Sunny Boy Storage inverter which would allow you to hook up a whole pack without having to rewire it to 48v like I did.
- The documentation recommend 10 to 5AWG wire to the AC terminal block. With 80A breaker, I am planning on using a 2AWG Aluminium (Will put the battery in a shed away from the house so need a more flexible cable that copper). Will I get into an issue trying to get this wire in the AC Terminal block ?
- Yea, you'll never get 2 AWG into the crappy plastic block the inverter Comes with. Take a look at some of my pictures, I skipped the block and connected directly to the breakers inside the unit.
- The max Battery charging is 120A for the 15kWh and I am assuming that the max discharge would be 15000/48 = 312A.
What size battery cable would you need for this ?
- You'll have to reference a couple things, first is the NEC allowed ampacity for that amperage which you can find in the table below,
- Then you have to take into account voltage drop based on the distance of the cable run, you're most likely going to get into the kcmil numbers since 4/0 AWG isn't big enough for 312A even for short distances.
- Here's a good links with the math you'll have to do Wire Sizing Tool for 12, 24 and 48 Volt DC Systems
- Were you able to find a way to switch mode (Battery to AC Priority) through the RS232 ? I would like to put a scheduler that would only allow Battery Priority during the PG&E peak hours and switch to AC after 9pm (After peak hours) to maximize the battery life. If I understand correctly, you are using Relay Contractors to emulate that functionality. I was wondering if I could control this from a Raspberry PI.
- I think you're misunderstanding battery priority mode. On that mode the inverter will start on the grid, and stay on the grid until the power fails then it will switch over to battery and stay on battery until the battery gets low then it'll switch back to the grid and wait for another power outage. You can easily switch over the inverter to battery mode using a relay on the pi by soldering to the small board where the dip switches are BUT that won't give you the functionality you're looking for, you're better off leaving the inverter on grid mode and using a contactor to drop the grid during peak hours. Then when you want to go back on the grid close the contactor and after 15 seconds the inverter will go back to the grid.
- I have a doubt about the Max ByPass current through the Inverter. I read through the doc that for the 12kW it is 63A and for the 15kw it is 100A. Am I reading this correctly ? Should I then put 100A breakers on my ATS Subpanels ? (I recall we talked about 80A before.... getting confused.)
- Yep, you're correct. I couldn't find any 70A breakers so I had to use 80A breakers and size my cabling accordingly.