Yes, if you want it to be EASY. Probably a difference of 6 mph vs 8 mph, maybe not that big of a deal.The UMC 6-15 adapter fits into the 6-20 outlet.
You can install our site as a web app on your iOS device by utilizing the Add to Home Screen feature in Safari. Please see this thread for more details on this.
Note: This feature may not be available in some browsers.
Yes, if you want it to be EASY. Probably a difference of 6 mph vs 8 mph, maybe not that big of a deal.The UMC 6-15 adapter fits into the 6-20 outlet.
to install a 6-20 outlet/box thru pvc conduit using appropriate wire size ( #10 I think, but will verify BEFORE i buy).
I'm in a condo. The feed to the meter is underground to a transformer pad/enclosure. The meter feeds my 125A disconnect adjacent to the meter, then the wires go underground/under-pad to my garage where they enter the service panel. Short of pulling new wires from disconnect to main panel, not much I can do. Even then, both disconnect and main and disconnect panel have to be replaced. The main panel is marked max 125A.
I don't know why, but pulling a permit in my area an electrician is about $350 give or take. Highest in the county and maybe state... The person that posted adding a 240V 20A circuit seems to be the most plausible and cheap. I can do myself; no permit. That might be my best bet. Doing google on a 240v outlet yields quite a few options. That is where I may need Mr Fixit.
To charge at 16 Amps, buy Tesla's 5-20 UMC adapter. Then make a short 6-20P to 5-20R extension cord. Label it "CAUTION 240 V - for EV charging Only."
Good Luck,
GSP
8 miles / hour with 6-15 vs. 10 miles / hour with 6-20
It seems I've underestimated 240V charging at lower amperage. In my previous post I wrote a 20A circuit would replenish the 20 miles per day plus 60 additional miles. II'll update my opinion and say the best solution is the 6-15 outlet and Tesla's 6-15 adapter. That should give the OP plenty of miles overnight.I achieve (shown):
8-9 mph 12A@243V
12 mph 16A@243V
18 mph 24A@240V
I just had the electrician over to assess adding the 14-50 wall outlet. No go. My service panel is 125A and the ONLY addition I can make is adding ONE measly 115v 20A circuit. I would have to replace my house disconnect, wires from meter to main panel and the main panel itself to add a 14-50 at a cost of $4,000+. Not going there...
I have a dryer outlet 10-30 in the laundry room off of the garage, but I can't reach even backing in without some form of extension. Can someone be so kind as to tell me or link me to a extension cable/adapter that I could use? Otherwise, at the 115v 20A I might get 6 mph... Although that would probably work for during the week as my work commute is ridiculously short, weekend's mean a trip to a super charger for sure...
THX,
M
This is exactly what I did (except with a Cutler Hammer CH panel) to free up some extra breaker slots. I then fed a new 100 amp subpanel in my garage, which will give me more than enough extra breaker space for the future.The Siemens panel I have has breakers that are normal width and offer one 120v branch, but they also have a double breaker that fits two independent 120v branches in the same amount of panel space - call it one slot. By swapping out several normal width breakers and compressing several branches down into half the panel space you might be able to free up enough for a double pole 240v breaker for a hefty branch of your liking...