Thanks for all the replies. Is there an easy way to identify if I have 14 or 12 gauge wire running to this outlet?
You can install our site as a web app on your iOS device by utilizing the Add to Home Screen feature in Safari. Please see this thread for more details on this.
Note: This feature may not be available in some browsers.
Thanks for all the replies. Is there an easy way to identify if I have 14 or 12 gauge wire running to this outlet?
Oh, right, that's the part I was forgetting. Romex is generally used for in-wall, so yeah, that would have to be 12 gauge for the 20A circuits. So in other words, "he who shall not be named" was assuming illegal installation when he said "more than likely" 14 gauge on a 20A circuit, saying it would be wrong.You're technically correct in what you're saying, but it doesn't represent a common installation scenario in most homes.
14ga THWN or THHN IN CONDUIT could use the 75 or 90c rating and be good up to 25 amps.
However, most/all 120v branch circuits in residential homes are run with NM wire ("Romex"), thus they must use the 60c rating, which is 15 amps for 14ga copper.
So to move away from the misdirection and arguments.
Everyone is starting in the middle of the equation and missing the real question.
the real question is what is the distance of your daily commute? with that information, you will find out how much charging that you need. You can find the charge rates of different plugs at the Tesla Adapter page. The 5-15 adapter, which is a standard AC receptacle as you showed, can support 3 miles per hour. And if you plug in for 10 hours, that's 30 miles recharge overnight. If you can be plugged in longer, then you can charge more, up to about 40 miles for around 13 hours. .
If your commute is about 50 miles, then the 5-15 isn't probably going to be enough. The 5-20 can take you to about 52 miles in 13 hours.
(while I believe this was part of the contention, it is possible that a quad outlet could be replaced with a single 5-20 may replace it, but check with a qualified electrician before doing so)
If 50 miles isn't enough, then 14-30 or 14-50 or going to be your options, but are indeed much more expensive to install. And in some older units, may be near impossible to implement.
If the 5-15 or 5-120 don't solve your options, seeing that you are in LA, you have a multitude of options.
- Charge at work
- Charge at a J-1772 very near work or home. See PlugShare.com for locations
- Charge at Supercharger
Now, these aren't exclusive options. It is very possible that you charge on a 5-15 during the week, slowly dropping over the week and then top-off at a Supercharger when needed. This is absolutely fine and won't damage the battery.
Also, while initial few miles carry a little energy penalty, if you are travelling over 25 miles one-way, so, speed is a factor that you can control. The record, AFAIK, for the Model 3 is about 600 miles at 40 mph. so slowing down can give you a lot more range. Going 75 mph will result in utilization worse than the EPA numbers, which are at about 60 or so mph. Even dropping to 55 can be really advantageous.
In other words, the calculation starts from how much do you need rather than how much can I get. My wife charging on 120V 15A and only plugs in once or twice a week.
That 5-15 plug may be all you need. But I would suggest having a licensed Electrician check it out to make sure that it hasn't badly aged, possibly replacing the plug and breaker.
Easiest way would be to turn off the breaker (make sure you've got the right one and the circuit is actually dead before you proceed), then unscrew the cover plate and one of the receptacles to get a look at the wire behind it. You may be able to see markings on the wire, but if not, post a pic of it here - 14 vs 12 ga is pretty easy to distinguish by sight.
No argument here.I find it best to not try and speculate on peoples' intention, but rather what they actually say. What @AlMason actually said is incorrect, and unambiguously so.
This is not pure speculation.......95% or more of present day and past built houses were wired with romex and common 15 amp circuits would indeed indicate 14 gauge romex WAS used.Along those same lines I find "most likely was pulled with 14 gauge wire" to be pure speculation, without any supporting evidence. Yes, of course this should be verified before swapping receptacles.
But that doesn't make the first part of what was said any more correct - "the outlets shown are 15 Amp maximum and should not be not be powered by the 20 Amp breakers pictured". That's what I responded to, because it's wrong.
I'm feeling that having to keep responding to you.I feel like I'm hitting my head against the wall trying to make you understand why this statement is false. Let me try once more.....
That's kind of yes and no. In reality the internals of most 5-15 and 5-20 outlets from a manufacturer are built the same for parts and manufacturing simplification, so they are both physically capable of the same 20A level. But the different face plates, one with the T-shaped slot and one without, is a compliance mechanism to enforce if needed that the pins of a 5-20 specific plug will not fit into a lower 5-15 outlet. So, if a 15A circuit is being wired, it is required to use only 5-15 outlets to enforce that compatibility.A 15A outlet is rated for 15A, with a 20A pass through. That is to say that the 20A circuit is in continuance throughout the circuit, however the receptacle itself (the contacts) are rated for 15A continuously. Any single appliance with a 15A plug will not normally draw more than 80% of 15A, or 12A. The total circuit draw (multiple appliances - same circuit) can be 20A before the breaker trips.
Yes--code agrees.A 20A breaker used with 12awg wire can feed multiple 15A outlets, one example is the kitchen. The reasoning is so that today's demanding appliances, which draw more current, can be used with a 20A breaker without the worry of nuisance tripping. If more than a total of 20A were to be drawn from the circuit, the breaker will trip.
Let me see if maybe we are misunderstanding a little. Are you saying a 20A circuit needs to have at least one 20A outlet on it? That may possibly be correct--I'm not sure. But if you are repeating what I think you've been saying before--that 20A circuits must have only 20A outlets, then no, that is false. NEC very clearly spells out that 20A circuits are specifically allowed to have a mix of 15 and 20 amp outlets. So it's like a one way indicator. If you see a 5-20 outlet, yes, that does mean it is a 20A circuit. But if you see a 5-15 outlet, it might be a 15A circuit or a 20A circuit. You would have to check the wiring and breaker to find out.It should be noted that any circuit that is intended to be 20A must use a 20A receptacle.
This is not pure speculation.......95% or more of present day and past built houses were wired with romex and common 15 amp circuits would indeed indicate 14 gauge romex WAS used.
Thanks. I could not tell by sight, so here are the pictures. Can you folks tell if I have 12 or 14 gauge here? Also seems there is an unused set of wires, so not sure what that is about.
Hard to be 100% certain from the picture, but that looks like 12awg wire to me. This might help you with further identification:
How to Use Pocket Change to Determine Wire Sizes
Which might be relevant if the pictures provided by the OP showed a 15 amp breaker. They don't - they show a 20 amp breaker. Everything else about wire size and how things were installed and whether or not this was always a 20 amp circuit vs a 15 and if it was installed incorrectly is pure and complete speculation.
You are really trying our patience. It's not a hurried statement at all, and you are playing terrible rhetorical games with this. Read it carefully, and I'll parse it to make it easier:One more thing you need to consider when you make a hurried statement such as this.
He was simply stating that the basic fact we had is only what was shown in the pictures, which was just a 20A breaker and a 5-15 outlet. Everything else would be unknown.they show a 20 amp breaker. Everything else [...] is pure and complete speculation.
Besides your misquoting what he said, the "assertion" that he made was not speculation at all. He just said you were guessing. You were making guesses about wire size. You were making guesses that a previous homeowner might have hacked something non-standard. And for you to try to reverse that and accuse him of speculating is just gaslighting of the worst sort.Your assertion that "if it was installed is pure and complete speculation" is pure and complete speculation on YOUR part. Have you considered that [...]
To the OP - the answer to your question is: No, you cannot wire a 15-20R to the circuit connected to any of the pictured breakers. These breakers, assuming they are installed correctly, will be wired, most probably, with No. 12 NM-B. The 14-50R requires larger wire (No. 6). To install a 14-50R a new 50A breaker would have to be installed (possibly in a sub panel if your panel has no blank slots), a length of No. 6 NM-B, SE or No. 8 THWN (in conduit) would have to be run and the receptacle installed.
My observations about the pictures are as follows:
One of the receptacle needs to be shimmed to properly fit in that box; a (sober) electrician likely wouldn't have left it like that (though most other tradespeople probably would have). ...and if you've got a gen1 charger you may not be able to get the plug firmly seated in the wobbly plug.
The other of those outlets does not appear to be grounded; the charging box would refuse to work on that one...
I'm also not entirely sure but it looks like the wires were not looped around the screw posts in the way I always do it.
This is a great suggestion as it ought, theoretically, to deliver charging at twice the rate available from 120V. However, and this is quite interesting, the power converter in the car is evidently much more efficient with 240V in. The Tesla website says that 20A @ 120 V will give you 4 mph implying that 0.8*20*120/4 = 480 Wh must be delivered to the car for each mile it is to travel. OTOH 20A @ 240 V delivers 15 mph charge implying 0.8*20*240/15 = 256 Wh/mi. The charger is almost twice (1.875 times) as efficient at 240V. Thus charging rate will be almost 4 times faster (factor of 2 from doubling the voltage and factor of almost 2 from increased voltage converter efficiency) and this is, IMO, well worth doing. And it's not a big deal to do it if you know what you are doing and have a circuit breaker finder. Turns out these are only about $40 these days. You need this gadget to find all other receptacles on the charging circuit. There probably aren't as the breaker in the panel is labeled "Master Bedroom TV Plug" which explains why the box is a quad and also suggests that nothing else is on that circuit but this needs to be checked. If there are any other receptacles they need to be removed and, of course, you lose use of them. The wires connected to them need to be spliced (with wire nuts or the new splicing connectors) such that removal of the receptacles does not break the continuity of the circuit. This goes for the neutrals as well as the hots and the neutrals need a bit of red tape around each one. Replace the cover plates with blanks. At the quad box remove both sets of plugs and replace one with a single 6-20R. Finding a cover plate for this arrangement on a quad box may be a bit of a challenge. Put red tape on the neutral (white wire) and don't cut it, or the black wire, because you will need to put everything back the way it was when you move out. Take pictures as you go.
- have someone inspect the rest of that circuit to make sure those are the only receptacles on the circuit, remove one receptacle and turn the other into a nema 6-20 and update the breaker to a 240v breaker and mark the ends of the wires to reflect that it is a 240 circuit. If you're renting, you'll maybe have to reverse this when you leave. You'll also need to buy an adapter for the mobile charger to get it to charge at 240/16amp