Hey there folks! My Model 3 has been ordered for a week and I am thinking about home charging installation.
I have done some research and googlin' but I am not totally confident in what I need and / or if it will work so here I go:
* Main box has 150 amp main breaker, 2 slots still open (next to each other) installing a 50 amp dual breaker
* Run is going to be 100 feet of 6/3 NM-B (sadly 125 feet since they don't see it in hundred feet runs)
*Nima 14-50 outlet
Any help is appreciated, really would rather not have to put out a ton of cash for someone to do it for me.
As discussed here, make sure to get a good quality receptacle. The Bryant is my favorite price/performance wise, but the Hubbell is probably the best (same company that makes Bryant). Then Cooper may also make a decent one Tesla recommended.
Lots of options of where to source wire from. I buy mine from Home Depot for simple projects like this. Any electrical supply house can hook you up. A friend of mine also likes these guys:
https://www.wireandcableyourway.com
Can you post more pictures of your panel? I want to see the stickers on the door with all the gory technical details. Optimally, pictures with the cover panel off are helpful too if you can do this safely. Also, take pictures of the path to the place you plan to install this and the final place of install.
That sounds like it would work out fine. You'll need to buy an adapter for the Tesla portable charger as it doesn't come with the 14-50 any more. Btw amazon will sell you 100' run of 6/3.
You can also do a 6-50 instead of a 14-50 as others have mentioned. The neutral is totally unused in charging Tesla's at 240v/208v (or any EV for that matter).
There are other threads here that discuss the importance of buying a quality 14-50 receptacle. I had already bought a leviton from Home Depot when I read them and ordered a bryant 9450FR (Amazon) . The difference in construction is amazing. The Bryant is going in the wall, the leviton went into the trash.
Precisely. ;-)
Given the limitations of power plugs and receptacles, I don’ know that you can get much beyond 40 amp service delivering 32 charging amps - it would depend on the specific charger you have. My new M3 was a replacement for a Leaf and we had the AeroVironment L2 30 amp charger on 40 amp service, we’ replaced it with a Tesla wired charger to get those last two amps and avoid using the adapter. Shouldn’t have bothered, I guess, but we did.
Sounds like 50 amps is either more than you need if you have an M3 standard(not necessarily baboon thing, oversized breakers have their risks), or not as much as you could use if you have an M3 LR or better - assuming you have a hardwired wall box or one with a suitable plug. Copper conductor size is a straight up lookup of current vs. distance... I don’t have that at hand so can’t comment on that. IMHO, thicker is better, I hate ‘at the margin’ setups.
You can draw 40 amps on a NEMA 14-50 or 6-50 receptacle if you have sufficient gauge wire and a 50a breaker (40a is 80% of 50a since you have to derate it). As others have mentioned, the UMC Gen 2 that comes with the car is limited to 32a. But UMC Gen 1 units and other manufacturers of EVSE units can charge at the full 40a.
I would not be worried about any wire size that meets the minimum code requirements and that is installed properly. The code calculations are intentionally very conservative.
Initially its just going to be the portable (with purchasing the additional plug)
Doing some additional reading looks like I might need to run UF cable since it will be going outside for @5 feet or so before going into the basement and then into the garage. Safe assumption ill need to run that through conduit?
Hrm, very good callout. This is a very good point. Wire in conduit outside is always considered a wet location and NM cable (which has paper inside of it) is not considered acceptable for wet locations.
You are allowed to run NM cable (romex) in conduit, but it is a bit goofy (sometimes it is just what needs to be done).
Trying to do the entire run in UF due to that 5' would suck. You totally can do THHN/THWN-2 in conduit and that is rated for wet (hence the W in THWN-2).
Might I suggest you include a photo of your breaker box?
And a more detailed description of where the wire will go?
Sounds like your breaker box is outside with the empty slots.
You intend to run a short piece of conduit from the box down to the basement?
From there, you plan on going through the house. Exposed? Ceiling?
Then into garage perhaps? Inside a wall? Finished or not?
You are allowed to run Romex in a conduit for short distances for purposes like this in many jurisdictions - it's kinda up to the inspector.
Yes, more pictures would be great!
Note that I am a huge fan of conduit if you can figure out a way to do it. I ran my Wall Connector wiring in 3/4 in EMT conduit and ran 6 AWG copper inside of it with a #10 ground. 60a breaker, lets me do 48a to the car. In your case, you could do this and then put a 50a breaker since it can't be over the receptacle rating. For your run it may be a lot more work though.
So its going from this outside box down into the basement (unfinished) then from the basement into the garage into a wall mounted Nema, nothing fancy. Literally the only outside portion is potentially this, I might be able to fish it through the existing tube but its pretty full.
I plan on buying an adapter at the service center when I go,
Note that there are all sorts of requirements about if you have to run the wire through studs, or you can run it below the studs (if over a certain size), etc... Check these out before you run the cable! I forget the rules on 6 AWG.
Congrats on the new car! Please report back on your solution!