If you haven't run this test, recommend you do so, if you want to be sure you'll be able to run off-grid when the PowerWalls are fully charged (such as when Storm Watch has been triggered).
Our system has been running for about a month. I fully charged the PowerWalls yesterday (99%) and while the sun was out, took the system off grid by throwing the breaker inside the Tesla Backup Gateway panel.
The system correctly switched over to PowerWalls and shutdown the microinverters providing solar power (since there was nowhere for that power to go).
But, when I went inside, every UPS system had a warning alarm or had turned off (and refused to turn on). One of our air conditioners failed to start.
And when I restored grid power, I encountered several problems with getting the system back to normal, and draining down the PowerWalls to the reserve %.
Tesla confirmed the off-grid/full PW power frequency was too high (our microinverters should turn off at 60.5Hz). Our problem has been escalated to "tier 2" support, and should see them reconfigure our Gateway to use a frequency closer to 60Hz in the next few days.
If you haven't run this test and you want to have confidence the system will work correctly (when you need it), you should consider doing this test.
NOTE after running this test, I found that one of our UPS boxes refuses to come back on, and the breaker was thrown during test in the bedroom where we have exercise equipment. Hopefully (other than the UPS) we won't see any other equipment damaged by the high frequency power...
Our system has been running for about a month. I fully charged the PowerWalls yesterday (99%) and while the sun was out, took the system off grid by throwing the breaker inside the Tesla Backup Gateway panel.
The system correctly switched over to PowerWalls and shutdown the microinverters providing solar power (since there was nowhere for that power to go).
But, when I went inside, every UPS system had a warning alarm or had turned off (and refused to turn on). One of our air conditioners failed to start.
And when I restored grid power, I encountered several problems with getting the system back to normal, and draining down the PowerWalls to the reserve %.
Tesla confirmed the off-grid/full PW power frequency was too high (our microinverters should turn off at 60.5Hz). Our problem has been escalated to "tier 2" support, and should see them reconfigure our Gateway to use a frequency closer to 60Hz in the next few days.
If you haven't run this test and you want to have confidence the system will work correctly (when you need it), you should consider doing this test.
NOTE after running this test, I found that one of our UPS boxes refuses to come back on, and the breaker was thrown during test in the bedroom where we have exercise equipment. Hopefully (other than the UPS) we won't see any other equipment damaged by the high frequency power...