As Mongo mentioned, the original 200 amp panel would only have a 200 amp breaker (no other breakers). All of the circuit breakers would move to the new 400 amp panel. This is the configuration for 2 PWs with all circuits backed up. With a single PW installation, the original main panel would be derated and only contain the circuits above 30 amps. The backup subpanel would contain the backup circuits that are less than 30 amps each.
Maybe you talked to the same contractor that I just talked to. He wanted to install a 400A subpanel, and I when I questioned him about it, he said the the additional current from the two powerwalls necessitated either a larger panel than my current 200A panel, or the main panel could be derated by installing a smaller service disconnect breaker. I don't have a formal proposal from him, yet, but he said derating the main panel would only save a few hundred dollars.