Thanks for the link. Maybe that's where the 5" discrepancy comes from. Perhaps the top can be up to 79" but the switch is at 74"?It is on the right side according to page 6 of the manual: https://www.tesla.com/sites/default/files/pdfs/powerwall/powerwall_2_ac_owners_manual.pdf
Exception No. 2: Switches and circuit breakers installed adjacent to motors, appliances, or other equipment that they supply shall be permitted to be located higher than 2.0 m (6 ft 7 in.) and to be accessible by portable means.
In case anyone needs an NEC reference for the 6' 7" rule on switches, it is 404.8(A). However, that section has an exception that seems to fit the Powerwall:
And I don't see anything in Article 705 (Interconnected Electric Power Production Sources) that would require a disconnect at the Powerwall itself that might be subject to more stringent requirements. So I'm not clear on the source of this height requirement for the switch on the Powerall.
Cheers, Wayne
I just found out that Tesla allows only a 3 ft maximum install height from the base of the Powerwall. This requirement, in my mind, seems to be procedural (available equipment and manpower factors) and safety related (lifting equipment, usability, OSHA, etc.).Isn't that meant to cover switched disconnects for high mounted thing like overhead doors motors or radiant heaters "adjacent to". The Powerwall would seem to be an integrated switch. It may be a usability induced requirement vs a code requirement, especially given the owner's manual references to power cycling it.
Yes, in my case a single panel as you described. However, Tesla, after the meter, ran the directly to the switch and then back to the main panel 200A breaker. This way they did not need a second panel. Not sure how to describe exactly what they did. Tomorrow, I can get a picture and annotate it. That said, Tesla brought power from the meter side into the breaker side, but bypassed all the breakers and ran the power then to their switch 200A breaker. They then ran the power back to my main panel to the 200A breaker that trickles down to the house breakers. This was the same as having basically an empty main panel running to the switch that then ran to a second 200A panel with all the breakers in it. This setup is working perfectly for me. Everything is powered correctly. Also, SCE had a planned power outage yesterday in my area that lasted over 8 1/2 hours. I was electrically isolated from the grid and ran off the batteries (and solar) without experiencing any problems. Keith
Yes, what you described is exactly what I have an it is 200 amps. So the process would be to move all of the breakers from my original panel to a surface mounted sub panel? Then all that would be left in the original panel is the main 200 amp breaker at the top? That sounds like what the contractor said and I was trying to figure out why since the Tesla installation diagram doesn’t show a subpanel for whole house backup. Does that mean that it can only be done that way with a different meter/main service panel configuration? BTW, if a new subpanel is added for whole house backup and contains all of the breakers, should/will it upgrade the service from 200 amps to something higher? The contractor mentioned a 400 amp sub panel but it isn’t specified as a 400 amp panel on the estimate.
Maybe you talked to the same contractor that I just talked to. He wanted to install a 400A subpanel, and I when I questioned him about it, he said the the additional current from the two powerwalls necessitated either a larger panel than my current 200A panel, or the main panel could be derated by installing a smaller service disconnect breaker. I don't have a formal proposal from him, yet, but he said derating the main panel would only save a few hundred dollars.
Now I am NOT an electrician but in doing my reading, with 200A from the grid, plus solar, plus PW you can overdrive the bus bars inside the panel so some advise upgrading the panel to have larger bus bars.Maybe you talked to the same contractor that I just talked to. He wanted to install a 400A subpanel, and I when I questioned him about it, he said the the additional current from the two powerwalls necessitated either a larger panel than my current 200A panel, or the main panel could be derated by installing a smaller service disconnect breaker. I don't have a formal proposal from him, yet, but he said derating the main panel would only save a few hundred dollars.
Similar situation here with 200A combination meter and load center. Tesla designed in a 175A "main breaker." (See optional read below) I questioned Tesla about this as I wanted to add more loads in the future (water heater circuit, 2nd EV charger). The explanation is from overloading the bus bars of the NEW backup loads sub-panel with solar and Powerwall. One of those ah-ha moments. Fortunately, their NEC load calculation is currently just under 175A.Now I am NOT an electrician but in doing my reading, with 200A from the grid, plus solar, plus PW you can overdrive the bus bars inside the panel so some advise upgrading the panel to have larger bus bars.
Now a very difficult way to configure a Powerwall installation would be to daisy chain all the panels, with the service disconnect at one end, and the Powerwall panel at the other end. Then all the panels need to be qualified under 705.12(D)(3). So this is a configuration to be avoided if possible.
The difficulty is qualifying the panel busbars under 705.12(D)(3). In a daisy chain configuration, every panel has to qualify, and the currents from the utility, batteries and solar (if present) add, design-wise.Is the difficulty you mention due to the possibility of the PWs backfeeding through the GW into the upstream panel?
The NEC isn't going to recognize such control mechanisms, what matters is the continuous inverter output current, 125% of that is the figure used for checking feeders and panel buses.If the PW/GW are configured as backup only (or with a main panel appropriate backflow limit via CT on service entrance), then there would not be the potential of overloading the main panel.
The inverter in each Powerwall is rated at 5800 VA continuous apparent power, which at 240V works out to 24.17 amps. 125% of that is 30.2 amps, but as the Powerwalls are connected via 30 amp breakers, we can round down to 30 amps. 30 amps per Powerwall is the figured required to be used for 705.12(D)(3) computations.If you have a dedicated backup panel, even with 4 Powerwalls, the most they will supply is 80 amps continuous.
@wwhitney - thank you for this write-up. It makes it clear why the drawings for my PowerWall install have separated the generation and loads. They are going to put the solar (2x20A 240V) and PowerWalls (2x30A 240V) in one "Generation Panel" on one load side gateway lug and the "Backup Panel" on the other load side gateway lug. I thought it would have been simpler to just put a breaker in the Generation Panel to feed the existing sub-panel which has all the backed-up loads, but the 100 amps of generation and 125A sub-panel breaker cannot go in one 200A panel.
Or could it? I would have 4 generation breakers at the bottom of the panel totaling 100 amps (solar + PowerWalls), in the middle is a 125 amp sub-panel load breaker, then the top of the panel would have the breaker that goes to the gateway. Could that be 125 amps? 225 amps of current source breakers feeding a 200A panel bus is less than 125%, but do the 4 breakers qualify as a source at one end of a feeder?
I currently have a 400A main panel with a 200A breaker from the meter and the 2x20A solar circuits at the bottom. They insisted that they be at the bottom, but for these purposes, the panel is so over-sized it doesn't matter.
Why would that be simpler? If the critical loads subpanel has a main breaker in your scenario, it is just one more breaker that is duplicative. If the critical loads subpanel would be MLO in your example, it's just shuffling breakers around.@wwhitneyI thought it would have been simpler to just put a breaker in the Generation Panel to feed the existing sub-panel which has all the backed-up loads
I would say yes. So a panel with a 200A bus, a 125A feed on the utility side at one end of the bus, and a 100A feed from alternate sources at the other end of the bus would qualify under 705.12(D)(3)(b)but do the 4 breakers qualify as a source at one end of a feeder?
I just found out that Tesla allows only a 3 ft maximum install height from the base of the Powerwall. This requirement, in my mind, seems to be procedural (available equipment and manpower factors) and safety related (lifting equipment, usability, OSHA, etc.).
Well, everything is just shuffling things around. I was trying to reduce equipment cost. The existing sub-panel has no main breaker, just the breaker feeding it in the main panel. That breaker and the feed has to be moved behind the gateway so it can be backed up. The install docs propose a completely new 200A panel on the outside of the house to "relocate loads" from the main panel. IIRC, the only loads that need to be relocated are this one subpanel and one bedroom AFCI circuit which also has my Enphase Envoy on it. So I am proposing eliminating one panel in the install and using only one load lug on the gateway.Why would that be simpler? If the critical loads subpanel has a main breaker in your scenario, it is just one more breaker that is duplicative. If the critical loads subpanel would be MLO in your example, it's just shuffling breakers around.
When they talk about stacked Powerwalls, don't they mean they are at the same level, like books in a bookcase with only one Powerwall attached to the wall and the others stacked in front of it?I think you may be right because a contractor (not Tesla) said that two PWs could be stacked on an outside wall which would place the switch on the top PW at about 85 inches. This is not a problem for me because if the top PW needs to be rebooted I could still reach the switch.